Domestic isolation query

Hi all,

I’m after some advice on a rewire I have been asked to install.

I am looking to relocate a consumer unit from under the stairs into the properties front door hallway.
My understanding, is that if I install a 100 amp switched fused unit, then I can just run a new 25mm 3core SWA to the boards new location.

However, my questions are, if I install this new fused unit, do I still need to put in place a 100amp DP meter isolator before the fused unit?

My second question is do I need to install an armoured cable to the new boards location, or can this be NYY cable instead. The route would be mainly through the floorboards.
I’m just concerned that the cable size would be awkward or difficult to direct through the joists up on the first floor.

Any guidance would be massively appreciated!

Chris
 
No you don't need an additional switch. I would avoid 25.0mm² SWA in a consumer unit the cpc will be oversized for the earth bar. If it is mainly through floorboards and doesn't need additional RCD protection just use 6181Y and a 16.0mm² cpc.
 
No you don't need an additional switch. I would avoid 25.0mm² SWA in a consumer unit the cpc will be oversized for the earth bar. If it is mainly through floorboards and doesn't need additional RCD protection just use 6181Y and a 16.0mm² cpc.
That’s a good point actually, I failed to consider the size of the earthing conductor.
The length of cable I need to move this board is approximately 18mtrs. Isn’t 6181Y cable just standard tails cables, and would this be ok under the floorboards or should this not just be 1 3core cable?
 
Yes, The 6181Y tails have just as much protection as any other grey sheathed cable like 6242Y Twin and Earth....

In fact, there was a rumour that 25mm twin and earth exists.... but its somewhere on the shelf next to sky hooks, glass rivets and a long stand.... :laughing::D
 
Yes, The 6181Y tails have just as much protection as any other grey sheathed cable like 6242Y Twin and Earth....

In fact, there was a rumour that 25mm twin and earth exists.... but its somewhere on the shelf next to sky hooks, glass rivets and a long stand.... :laughing::D
If only this was true, life would be so much easier
 
If it is to buried in the wall less than 50mm deep, another alternative would be 2 core 25mm swa.

it is only 20mm diameter and should not be to hard to wrangle round bends.

I haven't worked it out but you will need a 10 or 16mm earth cable run alongside it and the steel wire to be correctly terminated at both ends.

p.s. when i was a young lad on a canoeing trip, i did get sent to the leader in the furthest away boat to ask for a long paddle he sent me to another instructor because it was not in his boat, rinse and repeat, yes i was a bit thick and took them far too literally.

I think the bar stewards call it character building!!!!
 
What is the earthing system?
If TT, then you'll need some fault protection for cable.
Also, will the cable be buried in the wall at any point, even just a little bit? If so, you'll need mechanical protection as well if you use NYY.
You've mentioned a 100A switched fuse. Do you mean the switch will be rated at 100A, or the fuse will be 100A. If the latter, then it needs to be less than the cut out fuse size to obtain selectivity (or discrimination... I always get the 2 mixed up!)
 