freddo ~ Arms Supporter Oct 27, 2018 #2 Maybe. What is the current of the things, and what is the mode of operation? The last of this soft of thing we fitted was wired in FP200.
Maybe. What is the current of the things, and what is the mode of operation? The last of this soft of thing we fitted was wired in FP200.
C cliffed ~ Arms Oct 27, 2018 #3 Yea that’s what I thought,Fp,but wired in alarm cable. They are released from a FA relay.the loading of these 90ma nominal current
Yea that’s what I thought,Fp,but wired in alarm cable. They are released from a FA relay.the loading of these 90ma nominal current
westward10 ~ Staff member Admin Esteemed Supporter Oct 27, 2018 #4 Why would you want to connect them with alarm grade cable, seems rather non conventional.
westward10 ~ Staff member Admin Esteemed Supporter Oct 27, 2018 #6 Are they using these cables as part of the fire alarm auxiliary control.
C cliffed ~ Arms Oct 27, 2018 #7 westward10 said: Are they using these cables as part of the fire alarm auxiliary control. Click to expand... They supply power to the door opening,through a fire alarm relay. 24 v dc from a separate psu,through relay to door. It’s not an auxiliary contact
westward10 said: Are they using these cables as part of the fire alarm auxiliary control. Click to expand... They supply power to the door opening,through a fire alarm relay. 24 v dc from a separate psu,through relay to door. It’s not an auxiliary contact