Not had chance to read through yet, but i do hope you like green :D

DPC BS:7671/AMD 1 - The IET
 
It seems that they intend to rename the IEE Wiring Regulations the "IET Wiring Regulations".
 
Woo hoo!!!!!

No more RCD's on additions or alterations to circuits!!!!

Providing a few conditions are met of course :rolleyes:
 
It also seems that consideration should be given at switches for a neutral conductor to accommodate electronic devices (whatever they are).

Plus, local isolation is no longer needed for motors??????

If that the case, then we no longer need to install fan isolators.
 
Last edited by a moderator:
god sake , no sooner get things right in head ...... :)

anybody want to read it and post the main changes? :)
 
Last edited by a moderator:
It also seems that consideration should be given at switches for a neutral conductor to accommodate electronic devices (whatever they are).

Plus, local isolation is no longer needed for motors??????

If that the case, then we no longer need to install fan isolators.


hows that work say if the emergency stop button fails?

when is these changes coming in
 
thats ok then ill have done my 17th by then or do i have to go for another update course when this comes out
 
ok, heres one about the motors, although it does also remove the need for "a single point of isolation".

132.15 Isolation and switching Deleted by BS 7671:2008 Amendment No 1

132.15.1 Effective means, suitably placed for ready operation, shall be provided so that all voltage may be cut off from every
installation, from every circuit thereof and from all equipment, as may be necessary to prevent or remove danger.
132.15.2 Every fixed electric motor shall be provided with an efficient means of switching off, readily accessible, easily
operated and so placed as to prevent danger.




Note that the above has been crossed out in the DPC.


I have also moved this to the pub as we are not allowed to quote the document yet.
 
Last edited by a moderator:
Bit more:

Use of RCD's

........An exception to (i) is permitted for:

minor works associated with existing socket-outlet circuits not provided with additional protection by means of
an RCD where the designer is satisfied that there would be no increased risk from the installation of the addition
or alteration. The decision shall be recorded under part 2 of the Minor Works Certificate or the comments section
of the Electrical Installation Certificate (see notes 1 and 2).


Note 1: For minor works the installer is often the designer of the addition or alteration.
Note 2: The recording of this decision does not constitute a departure from this Standard


There goes the choc boxes :D

421.7 Every termination of a live conductor or connection or joint between live conductors shall be contained
within an enclosure selected in accordance with Regulation 526.5. Deleted by BS 7671:2008 Amendment No 1




514.10.1 8.1 Every item of equipment or enclosure within which a nominal voltage exists exceeding 230 volts exists and
where the presence of such a voltage would not normally be expected, shall be so arranged that before access is gained to
a live part, a warning of the maximum voltage present is clearly visible.

Where terminals or other fixed live parts between which a nominal voltage exceeding 230 volts exists are housed in
separate enclosures or items of equipment which, although separated, can be reached simultaneously by a person, a
notice shall be secured in a position such that anyone, before gaining access to such live parts, is warned of the maximum
voltage which exists between those parts.
Means of access to all live parts of switchgear and other fixed live parts where different nominal voltages exist
shall be marked to indicate the voltages present.
- crossed out.

Im not sure how the above is going to work?
 
Last edited by a moderator: