Hi.
We are looking at installing a Wiser smart heating system inc. trvs
We are currently electric only, with normal rads and a Heatrae sadia electromax combi boiler doing hot water and central heating duties.
Control is via a danfoss tp5000 battery programmable thermostat. This is only a two wire unit. No industry standard back plate so I know I need to wire a backplate for the wiser.
Looking at the wiring diagrams for the boiler and wiser system I believe I need to run a live and neutral from the boiler to the wiser. Is this 240… seems excessive if so, but where best to pick it up, 24 hour on (on boiler) perhaps. Then feeds to HW on and CH on on the wiser backplate. Are these simply reusing the room stat L and room stat R feeds that are currently used for the switching by the tp5000?
Thanks for any thoughts in advance!
 

Attachments

  • 9650B687-8473-469C-913E-C110809D9919.jpeg
    9650B687-8473-469C-913E-C110809D9919.jpeg
    390.1 KB · Views: 6
  • 991B50EF-82F7-42ED-A63A-0265CC493B75.jpeg
    991B50EF-82F7-42ED-A63A-0265CC493B75.jpeg
    356.5 KB · Views: 6
  • C42714B7-6560-46F1-BA6F-B1C54E2CC98E.jpeg
    C42714B7-6560-46F1-BA6F-B1C54E2CC98E.jpeg
    480.3 KB · Views: 5
  • 97C0BD2E-BA4D-4597-B0AB-1CF8580CB234.png
    97C0BD2E-BA4D-4597-B0AB-1CF8580CB234.png
    251.8 KB · Views: 6
A combi boiler doesn't require any hot water signal from the wiser controls as it operates on-demand.
 
It looks like you need the single channel version of the wiser control, this will need a permanent mains supply and its switched output connected to the heating L and R of the boiler.
 
Ah interesting. Assuming then that the hot water heats as required solely on the off peak feed unless the boost button is pressed then on 24 hour. Think I was confused by the diagram for the room stat L and R as one appears to go to the CH switch one to the HW switch
 
So second look without being an idiot… on the single zone wiser backplate terminal N and L to boiler N and L (pick up from main boiler supply or 24 Hour N and L?) terminal 1 to Room stat L on boiler and Terminal 3 to Room stat R on boiler? Then hopefully job jobbed?
Thanks
 
So second look without being an idiot… on the single zone wiser backplate terminal N and L to boiler N and L (pick up from main boiler supply or 24 Hour N and L?) terminal 1 to Room stat L on boiler and Terminal 3 to Room stat R on boiler? Then hopefully job jobbed?
Thanks
Yes that is the way to do it
 
Perfect thanks for reminding me I wasn’t paying attention!
Any preference on where to pick up the N and L? The 24 Hour terminals on the boiler are easier from a wiring perspective than the main boiler L and N being in the same block as the room stat terminals
 
The 24 hour terminals would be my preferred point to connect the L & N
 
Perfect. Mine too. Thanks
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Dorset
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Drayton wiser to electromax boiler
Prefix
N/A
Forum
Central Heating Systems
Start date
Last reply date
Replies
8