G

Guitarist

Just a quick one...
Been asked to connect a dual element tank, but as no eco 7, the customer wants to be able to switch both elements on together to heat the water up fast. Each element will have its own 13amp SFCU for switching from a its own 16amp MCB.
Anyone see a problem with this?
 
Can't see any problem with that like Guitarist. Apart from the running costs!

Usually the bottom immersion goes on the E7 and the top one on a pactrol timer on the peak supply, but no E7, yeah just run them the way you suggested.
 
Just a thought.

Bottom immersion on a timer to heat up overnight and a pactrol timer on the top immersion to boost the temperature during the day? That way only one immersion on at a time may help reduce the running costs??
 
Last edited by a moderator:
Just a thought.

Bottom immersion on a timer to heat up overnight and a pactrol timer on the top immersion to boost the temperature during the day? That way only one immersion on at a time there by reducing the running costs??

How does this reduce running costs if no E7?
 
Can't believe I'm going to sacrifice my 2000th post to point out that......

If you haven't got E7, it doesn't matter how many elements you use simultaneously to heat the water, the energy used to get a body of water from 10degs to 70degs remains the same - 3kW for 1hr, 6kW for 30 mins or 12kW for 15 mins.....it's still 3kWh on the meter.
 
Can't believe I'm going to sacrifice my 2000th post to point out that......

If you haven't got E7, it doesn't matter how many elements you use simultaneously to heat the water, the energy used to get a body of water from 10degs to 70degs remains the same - 3kW for 1hr, 6kW for 30 mins or 12kW for 15 mins.....it's still 3kWh on the meter.

Point taken Rockingit.

Were you saving that 2000th post for something special? :wink5: :wink5:

Pass me coat!
 
LOL - not really, it was more a curiosity as to how it would get spent rather than 'saving' it.
 
Thanks for the replies people. I realise that it will be expensive to have them both on, although no more expensive overall, but it will heat the water up fast. :)
Just wondered if I'd missed something obvious.
 
I suppose you may consider that if it is heating the water very fast and the thermostat is set to say 70 on the lower immersion then it is possible you may get overheat cutouts on the higher immersion if thermal equilibrium is not established quickly but other than that can't see a major problem with your arrangement.
 
I suppose you may consider that if it is heating the water very fast and the thermostat is set to say 70 on the lower immersion then it is possible you may get overheat cutouts on the higher immersion if thermal equilibrium is not established quickly but other than that can't see a major problem with your arrangement.

I did consider the implications of how the thermostats would cope, but then again, it's no different to someone having the lower element on eco 7 and switching the boost on while eco 7 is still active.
It' the sort of thing tho which I'm a little concerned about.
 
Logic would suggest that as heat rises, the uppermost stat would click off first before the lower one keeps going. That might mean an 'over temperature' at the top of the tank until the second elements stat catches up lower down. The way around that problem would be just to have the elements switched via a 2p contactor fed from the top stat.
 
someone tell me a little about off peak supply.....

does it sill be used.. how do you go about using it, ive seen few places that had 2 elements obv 1 was off peak but not in action anymore...

can these be reconnected up
 
someone tell me a little about off peak supply.....

does it sill be used.. how do you go about using it, ive seen few places that had 2 elements obv 1 was off peak but not in action anymore...

can these be reconnected up

I've done this for people several times now. Quite often, if a house has a now defunct e7 board, it's a pretty painless job just to reconnect the whole board to the tails via Henleys, and hey presto the owner gets 3-4 'new' socket outlets at 16A each after a faceplate change and then sometimes the option to get flexibility in the water heating, particularly if they've got a split tank.
 