Has anybody got a good copy that you can read of the pocket guide for bathroom zones I checked the one in the stickies and it was not very good.

Also I do work for a couple of letting agents and have it a couple of snags that I need to bounce of somebody so here goes.
Gas service company rips away the undergrowth of external gas meter and declares on the report "No main earthing at the gas meter" so I had a look at it and there is no access to the meter but Telectrix pointed me in the right direction ie reg 544.1.2 that states

"The main equipotential bonding to any gas or water service shall be made as near as practicable to the point of entry of that service to the premises. Where practicable the connection shall be made within 600mm of the meter outlet union or at the point of entry to the building if the meter is external."

So yep I sussed this out as they need to dig up work but want to make sure I have the info at hand incase it comes to a fighting match.

Also EICR a company that does the HMO properties have put in an unsatisfactory on 2 points C2 screw missing from light switch ? and bathroom light fitting is the wrong IP rating yet this is a tenement house ie ceiling hight is 3.5 metres so this is outside the zone ie 2.25M am I right in saying this.

Welcome any comments
 
Also EICR a company that does the HMO properties have put in an unsatisfactory on 2 points C2 screw missing from light switch ? Petty. i'd have fitted a screw . and bathroom light fitting is the wrong IP rating yet this is a tenement house ie ceiling hight is 3.5 metres so this is outside the zone ie 2.25M am I right in saying this. i agree with you unless it's deemed unsuitable for the environment, irrespective of zones

 
thanks Telectrix it gets a bit wearing when you get the the well this is a major company and I am trying to explain that they needs to get their sales up so they in my view are bending the regs a bit to get more work
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
earth bonding and IECR
Prefix
N/A
Forum
Electrician Talk
Start date
Last reply date
Replies
4

Thread Tags

Advert

Thread statistics

Created
oldtimer,
Last reply from
oldtimer,
Replies
4
Views
41

Advert