Morning all. So just trying to refresh my grey matter but having a biff moment. Earth fault loop impedance with circuits protected by BS EN60898 type B circuit breakers. I know the tabulated values are in table 41.3, but for the life of me I’ve forgotten how to calculate if acceptable or not. So for example; 40A circuit breaker, measured Zs 0.5, maximum tabulated value 1.09. How do I get the corrected values and see if acceptable? Any help for my non firing brain would be greatly appreciated. TIA.
 
As in multiply the tabulated by 0.8 to account for increased resistance on the cable under load conditions?
 
The values in table 41.3 BS7671 need to be multiplied as above (0.8), the values within the on site guide have already been adjusted to reflect the 0.8
 
and don't forget Cmin. that takes another 5% off the max. allowed value. however. I'm skeptical about the 0.8 correction esp. in a domestic. the 0.8 assumes that cables will be running @ 70 deg.C. that is loaded to the max. If you go with the design current Ib, rare you'll see cables getting that warm, only on things like showers.
 

Reply to Earth fault loop impedance in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock