Hi guys im working in a collage at the moment there some refurbishment happening to a stair case as the building was built in 1950, basically im 2nd fixing it and have found a problem with the earth thats feeding the D.B i have feed the lights from, i have the switch feed connected, emergency feed for EM lights connected, neutral connected but as soon as the earth is connected it blows the fuse for the switch and emergency feeds. if i leave the earth out the lights work perfect. i disconnected the earth and turned the circuit on and the earth is giving a back feed of 60 volts. there is no earth to live shorts and no live to neutral shorts. Any one have any ideas ? i spoke to the maintenance sparks and he said the building have a neutral problem that no one can seem to find. Its like a broken neutral.

this is the board
001.jpg
 
If you are blowing fuses with the earth connected the last thing you should do is energise the circuit with the earth removed, irrespective of your meter readings you could have put others or yourself at risk, if the building has a neutral issue this should be addressed urgently and i would question the maintenance sparks competence for not resolving the issue and not making you aware of a problem before hand he could have put yourself in danger.
When you say blowing the fuse is it tripping mcb's... rcd's or HRC fuses?
 
I gather there's been no testing carried out here as the tester would of identified this problem before energising the circuit ask for any test sheets if not suggest an eicr be carried out
 
I just hope the collage doesn't run any electrical courses. Mind you they could offer "practical" fault finding!
 
there is no earth to live shorts and no live to neutral shorts

What about the other way?
Tell them to get the whole place tested out properly instead of them fannying about.
 
If you are blowing fuses with the earth connected the last thing you should do is energise the circuit with the earth removed, irrespective of your meter readings you could have put others or yourself at risk, if the building has a neutral issue this should be addressed urgently and i would question the maintenance sparks competence for not resolving the issue and not making you aware of a problem before hand he could have put yourself in danger.
When you say blowing the fuse is it tripping mcb's... rcd's or HRC fuses?