Why would you want to? don't the big bolts form a good enough connection? done any testing.

Not always,often the big bolts will do very little to aid continuity. The pipes are glass/resin or plastic coated with a non conductive gasket between flanges. Even older pipes are heavily painted and cant be relied on for decent continuity.

Apologise for the picture but I'm not a pipe fitter so don't normally take any pictures of them ! As you can see virtually zero continuity through bolts.
 

Attachments

  • 063.jpg
    063.jpg
    2.1 MB · Views: 44
WIMES is driven primeraly by 7671 and this issue is an equipotentil bonding issue.
Had a disagreement with an "Engineer in the past where we used M6 braided earth bonds for bonding tray work. Hes issue was " I dont think them braids are 6mm as they dont look as big as them 6mm G+Y conductors". My response whilst stuffing a Tech specification sheet for said braids was you are quite correct they are not 6 mm braids they are 4mm2 and if you would like to check 7671 the minimium size is ?" (can anyone guess).
I continued with the green and yellow conductors are 6mm2 but dont worry we shall not charge you for the extra 2mm unless of corse you insist on us changing all these bonding braids to 6mm2 G+Y.
Never heard anymore on that subject.
However when bonding across pipe flanges it does tend to be to long a distance for braids so 6mm2 G+Y it is.
 
Somewhere in the back of my mind is a story about an old ABB MagMaster not working because of bonding between flanges and they all had to be removed for the '5-before, 3-after min.' head diameter lengths? Something to do with ABB flow heads needing 'floating' slip-rings between gaskets, between flanges? I remember thinking it was funny as it contradicted what you'd think on bonding.
Maybe I'm recalling this incorrectly.

Still... In the industries I've worked in, on the Scotch-coat types of pipework that David provided a picture of above, the flange is normally drilled, tapped and a 6mm strap bunged in. If deemed necessary.

I agree with the comments above about this being a call for the lead engineer and bonding should be done in the priority order of medium, process, electrical.
Bonding for the sake of bonding is for the over enthusiastic. For me, it come back to the fundamental question of what is bonding for? And if it isn't for this, then it's not for anything.

(Disclaimer: I'm industrial electrical but mainly control. Ignore all of my bitter ramblings above.)

Cheers, SP
 
“Hot-Bolting” is a very common practice in the oil industry, prior to a shutdown or pipe changeout. Basically the pipe fitter will change every bolt in a flange, one by one until they are all swapped out for new. It means that come the shutdown they can change the spool or gasket etc quickly without having to worry about seized bolts. I had guys who spent many days doing this offshore!

To go back to the OP, an easy solution would be to just throw in a serrated washer between the nut and flange on each side of one of the threaded studs. Actually a useful method to ground Motors on skids, rigs or ships when the contractor has forgotten to run an earth cable.

The only reason I can see for bonding them is to prevent static build up where Highly flammable chemicals are used, but mostly if the chemicals are really explosive 5he pipes will be fully welded rather than flanged.but if it’s water - why bother.

I will add that my current employer has procedures that actually allow for welding on live crude lines (must be pressurized and with a certain minimum level of flow) - got to love the Middle East!
Very late to the party here, but looking into best practice for making and breaking bolted flange connections (usually guided by ASME for chemical processing / petrochem etc) and there is no mention of star washers in ASME PCC-1. Therefore, I assume they are not permitted - only standard hardened steel washers are. Wondering whether to outline this in company procedure that star washers shouldn't be used. If this was to be the case, what would an alternative method be to earth across flanges without interfering with the flange bolts?
 