Feb 7, 2023
59
102
108
Worcestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
I was replacing a socket that had a cracked face and as I took said socket off I noticed the armour was earthed by using BS951 clamps. I wasn’t expecting to see any earthing of the armour as the SWA was in a conduit drop to the socket.

I’ve never seen it done like that before but now I walk around the factory and automatically assume every SWA I see entering a conduit drop will have the armour earthed with the clamps. Never been referenced on any EICRs we’ve had done in the past.

I don’t like it as the SWA hasn’t been glanded, just been shoved down the conduit.

I took the conduit drops away and glanded the SWA appropriately with the use of Earth Nuts.

Is the use of BS951 clamps acceptable practice for the earthing of armour?

20240425_111419.jpeg
 
Certainly not good practice, and I’m surprised whoever did this didn’t think the earth terminal in the bottom right of a plastic box needed earthed too.
 
  • Like
Reactions: MaintenanceSpark
Certainly not good practice, and I’m surprised whoever did this didn’t think the earth terminal in the bottom right of a plastic box needed earthed too.

I have found a couple of those BG sockets with an earthed plastic box in the factory!

Luckily it's only one area that has the SWA dropped in conduit so I think I'll be amending those.

Cheers littlespark.
 
I was replacing a socket that had a cracked face and as I took said socket off I noticed the armour was earthed by using BS951 clamps. I wasn’t expecting to see any earthing of the armour as the SWA was in a conduit drop to the socket.

I’ve never seen it done like that before but now I walk around the factory and automatically assume every SWA I see entering a conduit drop will have the armour earthed with the clamps. Never been referenced on any EICRs we’ve had done in the past.

I don’t like it as the SWA hasn’t been glanded, just been shoved down the conduit.

I took the conduit drops away and glanded the SWA appropriately with the use of Earth Nuts.

Is the use of BS951 clamps acceptable practice for the earthing of armour?

View attachment 117685
BS 951 states that clamps to this standard are not intended for connection to the armour or sheath of a cable and requires the packaging of the clamp to include the warning “Not intended for use on the sheath or armour of a cable
 
I’m surprised whoever did this didn’t think the earth terminal in the bottom right of a plastic box needed earthed too.
Does it ?
 
  • Like
Reactions: ipf
Does it ?
Agree.
Why does it? ........Unless it's a pee taking comment!
And also agree about the bad practice.
Sadly, seem to come across this more these days. It's not a solid earth connection.
 
  • Like
Reactions: MaintenanceSpark
yes it was a pee-take...

I was commenting if someone was dumb enough to use earth clamps on armour, they might just be dumb enough to earth a plastic box.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Worcestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information