armour

  1. G

    UK Steel Tape Armour and Reduced Neutrals

    Hi, someone has ordered Steel Tape Armoured cable instead of SWA. Can I use this armour as a CPC the same as SWA or not and if so is there a table so that I can check the figures. Secondly, correct me if I am wrong but 3ph with a reduced neutral should only be used on a balanced load ie a...
  2. mak

    Question about earthing the armour of SWA

    If cpc core is present i.e. it's either 5 core three phase or 3 core single phase — is a banjo connected with a brass screw into steel trunking adequate to earth the armour(provided trunking is earthed to the earth bar)? Or would you put fly leads in between then a fly lead to an earth bar? Thanks.
  3. R

    UK Class II enclosure + gland recommendation for divorcing SWA armour at TT outbuilding/shed?

    As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring of a two core SWA supplying an outbuilding/shed. The supply to the property is overhead TT, so DNO provide phase and neutral only, a sub 20 ohm rod...
  4. Rockingit

    Tables for SWA armour cpc?

    In a former life on another forum as well as this one.... there were a whole heap of downloads that people had done as ready-reckoners for things like Cu eq for various armour sizes, R1R2 values on lengths.. useful stuff. I think I might even have generated some myself. Anyone have any...
  5. h.abrar94

    How to calculate the resistance of steel armour under fault conditions 70 oC for CSA 95mm2

    Hi All, hope your all well. I was hoping if I can please get some advice in regards to SWA. In Particular using SWA as CPC. Cable size 95mm2 I have a table for SWA which shows various information, in the last two columns it shows the "resistance of steel armour under fault conditions at 70...
  6. GBDamo

    2.5mm or 4mm SWA armour bonding

    Armour not CPC. By the letter of the regs 2.5mm is acceptable as the DB offers both mehanical and corrosion protection. Just seems a bit puny on a 10mm SWA, what about a much larger cable? Can some of the boffins explain why 2.5mm is deemed acceptable. Cheers
  7. Fitzy

    SWA outer armour not earthed at either end.

    A friend at work asked me to take a look at the electrics in his shed, RCD would occasionally trip out, turned out to be a very loose neutral going in to the RCD. One thing I did notice though was that the 10MM2 SWA entered through the back entry point of both the shed & house CU and neither...
  8. V

    SWA cable , TT, do i need an earth conductor in the cable?

    At the origin the installation is TT. Plan is to install a submain to a new db. Not carried out all the calcs yet, but my question is does the swa require an earth conductor in the cable. Basically planning on running a phase and neutral or perhaps even 2 x phases and neutral.(the cable will be...
  9. P

    High Zs on SWA Armour / New Earthing Conductor

    Hi all I am after some help/Advice if possible please A SWA sub main Distribution circuit has been given a Code 2 Rating on a recent EICR due to a high Zs of 2.8 ohms. The cable is 180 metres long and runs underground in ducting. The Install is from a few years ago when a new Substation was put...
  10. A032701

    How to connect SWA armour to 6mm Twin and Earth cable

    I have run 6mm t and e through the house from the db in the garage on a 32 amp mcb which is rcd protected. the 6 mm cable then goes into the back of an ip66 rated JB on the side of the house. i then intend to run 2 core (live and neutral) 6mm swa up to a workshop using the armour as earth. my...
  11. B

    Swa armour feeding TT system

    I have installed a TT system at my garage, and it is fed via 10mm 2 core armoured cable, does the armour of the cable have to be earthed via the supply tncs side or can it be glanded and earthed the garage side (TT). Anyone know the regs ? Thanks
  12. Wilko

    SWA Armour Use Descriptions

    Hi - various discussions we've had are summarised in this Voltimum information paper. Interesting for me was they effectively say main protective bonding in PME installations should be external to the cable, due to heating risk. I'm still digesting this myself ... The earthing functions that can...
  13. snipersmith87

    SWA cables - fly leading armour as cpc??

    Just after A bit of advice regarding a load of swa cables into dist board. What's people's preferred methods / good practice regarding banjos fly leads etc. Banjos inside?? If multiple cables are using armour as cpc is it considered bad practice to use 1 fly lead between the two Banjos??? Is it...
  14. C

    Testing ze with armour as earth

    Hello all, Quick bit of background, factory maintenance spark for 20+ years, covered some installation work over the years but not done a great deal of testing. New lines and cells are being installed over the next few months and all installation is being done in house. Decided it is time to...
  15. Sparky_marky2

    SWA armour supply to outbuilding, what CSA cable? and Reference Method?

    Hi guys, I am running a supply to an outbuilding that requires a 22m run from the Main CU (in the garage) to the CU in the outbuilding, at the Main CU it will be a 40A MCB supplying an 63ma RCD protected sub board which will then supply: 6A type B MCB for 12 downlights and an extractor fan 32A...
  16. H

    EICR Coding - Armour not glanded

    Doing EICR on a HMO, DB feeds a Consumer Unit in each room. The feeds to each consumer unit seem to be SWA however the armour is not visible/accessible at either the consumer unit or the DB - it seems to have been cut out behind the DB which is inaccessible. The cable is buried in the walls and...
  17. K

    Using SWA armour for earth on a sub-mains supply

    Hi all, long time reader first time poster. I am an apprentice that has mainly done domestic work, but more recently we have been doing commercial jobs (which i much prefer lol), i do really enjoy electrical work and I'm keen to learn more, which means i ask a lot of questions. The last couple...
  18. M

    Resistance per meter of armour

    I know it's late and the lap dances are still open , so i will wait till tomorrow for any replies . Does anyone have resistance per meter tables for steel armour 90degree thermosetting ,can't find it anywhere . Ta
  19. M

    Electrical installation design guide

    Have been sizeing up the size of armour on diffent SWA cables to make sure they are suitable to be protective conductors. Come across table 8.8 page 100 .on this table it says maximum bs88 fuse size (for example) 120mm 4core is 500a, when it also says current carrying capacity is 335 method c...
  20. D

    Supply to static permanent residence caravan

    Hi, looking for some advice for supply to static permanent caravan at bottom of garden. My House supply is TT. From what I can gather from previous thread s, is this acceptable. House end, SWA terminated into plastic ad.box and l+n tails into non RCD side of cu, from suitably rated MCB. Armour...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock