A friend at work asked me to take a look at the electrics in his shed, RCD would occasionally trip out, turned out to be a very loose neutral going in to the RCD.

One thing I did notice though was that the 10MM2 SWA entered through the back entry point of both the shed & house CU and neither end of the outer sheath was connected to the earth bar and was also very loosely pushed through at the shed end directly from outside of the shed. I thought that the outer armour of the SWA cable had to be earthed at at least one end, if not both? Am I right here?
 
Last edited:
Bulk Workwear - Clothing Suppliers for the Whole Forum Network
This official sponsor may provide discounts for members

Fitzy

-
Arms
  • Thread Starter Thread Starter
  • #3
Yes, it should be earthed, preferably at the supply end.
So one end is ok then?

I was thinking of adding the brass gland to the supply end, then run an earth fly lead to the cu early bar, is this ok?

Plus, is ok to use the back entry for swa cable, or should it always be glanced at both ends?
 

littlespark

-
Arms
Esteemed
Advent Win
Is there a core being used as the cpc inside the SWA?
The armour should be earthed at supply end at least.

10mm? What the heck has he got inside the shed?
or is that, what the heck is he growing inside the shed?
 
D

Deleted member 26818

If you need to isolate the earth, you can get special glands, or if it’s a plastic CU in the shed, just don’t use a banjo and fly lead.
 

Loki

-
Trainee
Supporter
Advent Win
10mm? What the heck has he got inside the shed?
or is that, what the heck is he growing inside the shed?
I’m suspecting they’re using a core back for earth. From what I remember tncs required either a 10mm earth or a tt spike near the shed.
 

Fitzy

-
Arms
  • Thread Starter Thread Starter
  • #9
Is there a core being used as the cpc inside the SWA?
The armour should be earthed at supply end at least.

10mm? What the heck has he got inside the shed?
or is that, what the heck is he growing inside the shed?
Yes, the black core has been used as the earth, the house’s supply is TN-S and the SWA run is roughly 30m in total. One light circuit and 2 socket radials in the shed.

Is it ok to go directly in through the back of the db, directly from outside? There’s been no mastic used to fill the rear entry hole either. I would’ve clipped the swa to the inside wall of the shed, then in to the db.
 

Andy78

-
Mentor
Arms
Esteemed
Yes glands should be used for proper termination. It's part of the cable system. You wouldn't use MI without a gland .......
 

Baddegg

-
Arms
Supporter
Esteemed
Advent Win
I would terminate into a wiska/adaptable box fitz and then from that to the Cu in t&e
 

Fitzy

-
Arms
  • Thread Starter Thread Starter
  • #12
I would terminate into a wiska/adaptable box fitz and then from that to the Cu in t&e
I did suggest re-routing the swa to the inside wall, then glanded in to the shed db, luckily there’s enough slack in the swa to still reach the db from inside, then i’ll fill the hole in shed wall.

It was only done last summer by an electrician friend of a friend.
 