Been asked to do some rewiring, and have said needs upgrade of consumer unit really
Main question is regarding earthing - Zs reads at 0.45 ohms (which suggests at TNS) But cannot see where earth cable goes to from old fuseboard.
There is no earth to fuse carrier or cable to fuse carrier in house.
Im guessing it goes to neighbour, and they actually have a looped supply.
Current cable is not even 10mm - and if earth is back to neighbours incoming supply - I guess I’d need to ask DNO about getting it switched to inside the clients house?
I can’t access neighbour to confirm all this conjecture - but have asked client to talk to them and get me a pic of their incoming supply