S

Stuart Houghton

My customer wants to have one ring main connected via a change over switch to a generator.

Earthing is TNCS

My idea was is move the ring main to a new consumer unit run a 6mm T&E to the change over switch from the 32 amp mcb in the main C/U where the ring main was. Then a 6mm T&E back from the change over switch to the new C/U.

I would install an earth rod which would be connected to the new C/U so the new C/U would have two earths one from the existing C/U and one from the earth rod.

The house is in a village with lots of overhead wires and I just thought what would happen if the neutral was brought down by a tractor then the return current that would normally go down the neutral of all of the houses after the break would be back fed through my customers C/U through the ring mains T&E and to ground via the earth rod. This could easily be a very high current which would surely melt the earth wires of the ring main.

Am I missing something ?
 
How would the diverted neutral current flow via the cpc of the ring?
it would flow down the neutral after the break into my customers house at which point the neutral and earth are linked together, then to the existing C/U then to the CPC of the ring which is linked to the earth rod.

Hope that make sense !
 
try TT system.
Not sure what you mean. I need to provide an earth which I am doing using an earth rod and the house is TNCS. I don't think I can switch the Earths as part of the change over switch so the TNCS will be connected to the earth rod as well. The generator will be a small 2kw portable type.
 
so you are using the earth separate ?
Sorry still don't understand what you mean. The earthing will be be 6mm from existing consumer unit to new consumer unit then 6mm from new consumer unit to the earth rod. That way its earthed when there is a supply from the grid and earthed via an earth rod if the grid is completely lost. Grid connected it will be TNCS, generator connected it will be TT.
 
Sorry still don't understand what you mean. The earthing will be be 6mm from existing consumer unit to new consumer unit then 6mm from new consumer unit to the earth rod. That way its earthed when there is a supply from the grid and earthed via an earth rod if the grid is completely lost. Grid connected it will be TNCS, generator connected it will be TT.
now the I get the story.
 
My idea was is move the ring main to a new consumer unit run a 6mm T&E to the change over switch from the 32 amp mcb in the main C/U where the ring main was. Then a 6mm T&E back from the change over switch to the new C/U.

I would install an earth rod which would be connected to the new C/U so the new C/U would have two earths one from the existing C/U and one from the earth rod.

The house is in a village with lots of overhead wires and I just thought what would happen if the neutral was brought down by a tractor then the return current that would normally go down the neutral of all of the houses after the break would be back fed through my customers C/U through the ring mains T&E and to ground via the earth rod. This could easily be a very high current which would surely melt the earth wires of the ring main.
Sorry still don't understand what you mean. The earthing will be be 6mm from existing consumer unit to new consumer unit then 6mm from new consumer unit to the earth rod. That way its earthed when there is a supply from the grid and earthed via an earth rod if the grid is completely lost. Grid connected it will be TNCS, generator connected it will be TT.

Am I missing something ?
Sorry still don't understand what you mean. The earthing will be be 6mm from existing consumer unit to new consumer unit then 6mm from new consumer unit to the earth rod. That way its earthed when there is a supply from the grid and earthed via an earth rod if the grid is completely lost. Grid connected it will be TNCS, generator connected it will be TT.
 
it would flow down the neutral after the break into my customers house at which point the neutral and earth are linked together, then to the existing C/U then to the CPC of the ring which is linked to the earth rod.

Hope that make sense !

But that wouldn’t flow through the cpc of the ring circuit, it would flow via the earthing conductor and cpc to the changeover switch, then to the essential services CU, then to the earth electrode.

Whatever position the changeover switch is in, as you have described it, the route from the N-E link in the cutout to the earth electrode will always be via the 6mm T&E’s rather than via any final circuit.
 