Not applicable here, but on a larger standby set, where there is an N-E link, am I correct in thinking the generator earth should be connected to the MET of the installation? (as there will be times when both genset and DNO supplies are energised concurrently, e.g. after the DNO supply is restored following an outage, prior to the AMF changeover switch reverting to the DNO supply)
 
I think that the ideal situation is to have the earth switched as part of the changeover arrangements, otherwise a fault in the installation might give a DNO operative a rather nasty surprise.
 