Hi I have come across something today that I have not encountered before, the tails from the service head went into a Henley's blocks then onto the consumer, the earthing conductor was taken from the consumer straight into the neutral Henley's block. The service head did have pme sticker on it. I have only ever seen this joined through at the service head.
measure your PSCC and PEFC. if they are the same, you have confirmed it's probably PME, but i'd get DNO in to do it properly.
Cheers for that I have done work in the house next door, & that is p.m.e. The consumer was changed 2 years ago and not an rcd in sight, so this rang alarm bells for me.
This is/was fairly standard practise from a local DNO around here, it wouldn't concern me in the slightest as it has a sticker, as has been said just check your PFC and pscc
I wasn't concerned as I believe it to be like others in the street, which are p.m.e. I just thought it a bit unusual. Cheers for replies.
probably DNO being too idle to fit a cut-out with earth terminal.
The area I work in covers both Northern Power Grid and Western Power, I have only seen the above arrangement with Western Power installs and it seems to be common practice in this area, for the earth to be taken from a henley block rather than the service head.
SNAP - standard western power practise I think, I have never seen it in any other areas!