When changing a consumer unit how many of us install new earth to gas and water this is something I've always done myself but I'm hearing quite a few sparks in my area are adopting the adiabatic formula and if calculations are ok there not up grading eaths to water etc herd one say its a pig of a runn from board to water intake so I used adiabatic formula and the 4 mm that was in was except able your thoughts guys
 
I would say its perfectly acceptable to use the adiabatic like you say, however i am with you and always upgrade anyway. Gives better peace of mind, plus any half assed assessor or building control cannot argue then
 
I'm pretty sure you can't use the adiabatic as its only meant for protective earths not bonding.... I could be wrong
 
You can use a diabetic to calc the main earth then half that must be bonding

You will be surprised of the small size actually required

However the minimum for both is 6mm so in your case it doesn't comply

This is also not an option for pme systems where selection of table 54.8 (ithink that it)must be used

For 99% of domestic tt and tns supplies, 6mm earth and bonding is totally compliant...........all that 16mm earth and 10mm bonding cable is totally unnessacary! And is only required for pme supply
 
Last edited:
My understanding is that tn systems are the same.... The adiabatic is just for protective conductors whether it be main or cpc's. bonding is totally different and do different jobs. You will have to refer to the bgb. But 6mm is min I think for both as welchboy said.
 
has it always been possible to install new earth cables on every consumer unit you have changed farmelectrics , as i find this hard to believe
 
Surely it's always possible to replace earths and or bonding, but some are just more involved than others.
6mm minimum if existing, pme systems require 10mm Iirc
 
I agree rampant chillii
After all if there was no bonding at all then you would have to run a bond back to the board somehow regardless of how much of a mission it was...... well i would anyway!!!
 
It's a bit like the old "practicable" excuse. If it involves any effort, then many don't bother.
 
My understanding is that tn systems are the same.... The adiabatic is just for protective conductors whether it be main or cpc's. bonding is totally different and do different jobs. You will have to refer to the bgb. But 6mm is min I think for both as welchboy said.

No this is not quite right

you can use table selection sizes or adiabatic equation for TNS/TT main earths

then as per regs the bonding conductors must be no less than half that of the MINIMUM required earthing conductor(through calculation or selection methods) AND not less than 6MM

thats why there are such skinny little earth tails soldered onto TNS cable sheaths by the DNO

you cannot use the adiabatic equation for a TNCS(PME) main earth as this is sized according to the suppliers neutral conductor, in the event of a lost supply neutral the main earthing and bonding conductors will potentially be carrying network current and must be considerably larger
 