Hi everyone!

I put it in an outside socket and light ran off of an internal Fused Connection Switch for isolation purposes due to shared access. I now wish to run SWA from this socket to a double socket in my small aluminium shed to power my tumble dryer.
Currently using extension lead which is a pain and not ideal electrically.

My main concern is earthing of the shed, how do I 1. Feed SWA into the shed, simple drilled hole and grommet job?
And do I mount the socket to a wooden block inside and/or have a fly lead of earth onto the sheds interior from that socket. Anything else I'm overlooking or missing?

Oh it's is a TN-S supply as well.
TIA
 
Last edited:
Will require a DB/CU & TT Earthing system, the metal shed will need a Protective bonding conductor connected to it.
Disregard Cpc from house @ shed & use new earth, SWA will be protected by protective device @ house DB/CU.
Obviously RCD/RCBO’s required , this is one option & most probably the best😎
 
Will require a DB/CU & TT Earthing system, the metal shed will need a Protective bonding conductor connected to it.
Disregard Cpc from house @ shed & use new earth, SWA will be protected by protective device @ house DB/CU.
Obviously RCD/RCBO’s required , this is one option & most probably the best😎
Thanks for the swift reply.
However, a few issues with this IMO. It's sitting within a courtyard garden area with main waste pipes and water etc running through that area, obviously fully concreted base so would be a lot of work to drill through that and get any sort of soil, it's extremely hard concrete and I also have young children playing in that yard as well so that's just another potential obstacle for them 😅 whole house was rewired 2 years ago to current regs, full RCBO board and SPD. I would earth SWA both ends and of course the FCU has a 13amp fuse, it's only about a 10m run if that to the shed Is there any other alternatives? :)
 
Thanks for the swift reply.
However, a few issues with this IMO. It's sitting within a courtyard garden area with main waste pipes and water etc running through that area, obviously fully concreted base so would be a lot of work to drill through that and get any sort of soil, it's extremely hard concrete and I also have young children playing in that yard as well so that's just another potential obstacle for them 😅 whole house was rewired 2 years ago to current regs, full RCBO board and SPD. I would earth SWA both ends and of course the FCU has a 13amp fuse, it's only about a 10m run if that to the shed Is there any other alternatives? :)
I see it’s TNS, because the shed is metal it needs earthing.
Being an extraneous conductive part it requires a conductor suitable .. 10mm is the usual size you may be allowed 6mm.
If the SWA size is the above then this would be acceptable.
You could put the Earth Electrode somewhere not noticeable, if needed 😎
 
I'd be testing the metal shed to see if was classed as an extraneous conductive part. If it's not then you wouldn't need to get a 10mm bonding cable to it.

As for earthing it
I see it’s TNS, because the shed is metal it needs earthing.
Being an extraneous conductive part it requires a conductor suitable .. 10mm is the usual size you may be allowed 6mm.
If the SWA size is the above then this would be acceptable.
You could put the Earth Electrode somewhere not noticeable, if needed 😎
It may not be an extraneous conductive part. I would be testing it to see if<23kohms. If it was well above that, i wouldn't be bonding. However, would it still be classed as an exposed conductive part and require earthing? I'm not sure. I would think it would
 
It is not an exposed-conductive-part as it does not form part of the electrical installation. Extraneous-conductive-parts do not form part of the electrical installation and metalwork will become such if it introduces earth potential which can be verified by testing. If it is sitting on a concrete base there is every chance it is not and as such would not require a main protective bond. Some have the mindset to bond it to make it "safer" but this is not necessarily the case. By bonding something that doesn't necessarily need it can result in currents running through it under fault conditions.
 
Last edited:
It is not an exposed-conductive-part as it does not form part of the electrical installation. Extraneous-conductive-parts do not form part of the electrical installation and metalwork will become such if it introduces earth potential which can be verified by testing. If it is sitting on a concrete base there is every chance it is not and as such would not require a main protective bond. Some have the mindset to bond it to make it "safer" but this is not necessarily the case. By bonding something that doesn't necessarily need it can result in currents running through it under fault conditions.
Agree & requires testing as said in above Posts😎
 
It is not an exposed-conductive-part as it does not form part of the electrical installation. Extraneous-conductive-parts do not form part of the electrical installation and metalwork will become such if it introduces earth potential which can be verified by testing. If it is sitting on a concrete base there is every chance it is not and as such would not require a main protective bond. Some have the mindset to bond it to make it "safer" but this is not necessarily the case. By bonding something that doesn't necessarily need it can result in currents running through it under fault conditions.
Good outlook. Testing would just involve a wander lead test?
 
It is not an exposed-conductive-part as it does not form part of the electrical installation. Extraneous-conductive-parts do not form part of the electrical installation and metalwork will become such if it introduces earth potential which can be verified by testing. If it is sitting on a concrete base there is every chance it is not and as such would not require a main protective bond. Some have the mindset to bond it to make it "safer" but this is not necessarily the case. By bonding something that doesn't necessarily need it can result in currents running through it under fault conditions.
Thanks for that Westward.

It's easy to determine if something is extraneous. You do a definitive test and get an answer? There is no such test for exposed conductive parts, it is just a definition.

What does it mean 'forms part of the electrical installation'? What defines 'part of'?

If you have sockets and lights plastered all over a metal building, what happens if the line ever comes into contact with the metal building under fault conditions, the 30mA RCD will not trip as there will be <10mA flowing to earth (if the shed is at >23Kohms to earth). If someone touches the shed they could easily be standing on the grass by the side of the metal shed and get a dangerous level of current through them. I think!
 
An exposed-conductive-part is part of an electrical installation which may become live under fault conditions whereby other means are not in place to prevent it coming live.
Cable tray and ladder systems are not deemed exposed-conductive-parts as they support cables which under fault conditions should not transfer that fault to them by having earthed sheaths or by having insulation and a sheath. If you have a steel conduit and run 6491X through it it becomes an exposed-conductive-part as you only have basic insulation preventing fault transfer, run an earthed sheathed cable or PVC/PVC cable through it you could argue it is no longer an exposed-conductive-part.
 
As I will be mounting on wood within the shed, and I will be using plastic weatherproof socket inside, can I just connect up and earth both ends of SWA I plan to use from another plastic outdoor socket and extend the PE?
 
As I will be mounting on wood within the shed, and I will be using plastic weatherproof socket inside, can I just connect up and earth both ends of SWA I plan to use from another plastic outdoor socket and extend the PE?
Still does not alter the fact we’ve been talking about😎
 
Thanks for that Westward.

It's easy to determine if something is extraneous. You do a definitive test and get an answer? There is no such test for exposed conductive parts, it is just a definition.

What does it mean 'forms part of the electrical installation'? What defines 'part of'?

If you have sockets and lights plastered all over a metal building, what happens if the line ever comes into contact with the metal building under fault conditions, the 30mA RCD will not trip as there will be <10mA flowing to earth (if the shed is at >23Kohms to earth). If someone touches the shed they could easily be standing on the grass by the side of the metal shed and get a dangerous level of current through them. I think!
Thinking if less than 2.3K, greater than no bonding required😎
 
But because it's TNS and all accessories are plastic etc isn't the risk of the shed becoming live almost zero if the neutral is separate from supply there's no risk to energize the potential earth?
No the risk is there by the difference earth potential of the metal shed, have you tested for an extraneous part?😎
 