No the risk is there by the difference earth potential of the metal shed, have you tested for an extraneous part?😎
But the shed frame isn’t connected to live parts, so touch voltage should be minimal no? I haven't tested yet but I'm going to assume because it's on membrane and concrete base it's going to be very minimal..?
1. You need to test to see if it's extraneous. It probably isn't, but 'probably' isn't good enough. If it is, then you have to run a separate 10mm bonding conductor out to it.
2. I can't quite get my head around not earthing (not talking about bonding here) a metal shed, as my fear is if the metal shed comes into contact with the live (line) conductor then the RCD wont trip and the shed rises to 230V potential to earth... I think.
3. @westward10 seems sure it's not an exposed conductive part which outweighs my thoughts in point 2 because he's far more experienced.
4. If this was my thread I would keep pushing for more responses and discuss further until I felt I completely understood the situation before I started doing any work. You need to be certain you are doing it correctly, not 'pretty sure'.
1. You need to test to see if it's extraneous. It probably isn't, but 'probably' isn't good enough. If it is, then you have to tuna separate 10mm bonding conductor out to it.
3. @westaward seems sure it's not an exposed conductive part which outweighs my thoughts in point 2 because he's far more experienced.
4. If this was my post, I would keep pushing for more responses and discuss further until I felt I completely understood the situation before I started doing any work. You need to be certain you are doing it correctly, not 'pretty sure'.
Absolutely agree, which is why I'm throwing back ideas and thoughts I'm having 👌 I'm sure that my plan has negated the chance of live parts being in contact with the shed itself and no chance of that happening it would be fine. I appreciate the feedback though, all helps towards a better understanding. I think I will definitely do a test on it. If it's a nice low reading I think I'll be confident enough to move forward with my initial plan of using the wood backing and plastic sockets etc. earth both ends of SWA to ensure continuity etc etc.
Adam, do you know how to test for extraneous? You've mentioned 'a nice low reading', which is the opposite of what you want.
I was thinking of a wander lead/ voltage test? Between the MET and shed
Yes, but you need to be clear whether it needs to be above the magic figure, or below it!
The clue is in HHD's post 5, but your comments since seem to have misinterpreted the value required 🤔
I was thinking of a wander lead/ voltage test? Been the MET and shed
I'm thinking of a potential difference test.
I think the test being described would be the continuity test. Both would have have opposite readings aka: above 22 for the continuity and then as low to 0 as possible for the potential difference test.
Please let me know if that thinking is correct and maybe where I've misinterpreted.
Yea No:2 it’s maybe an extraneous part & the reasoning for a bond connection, the shed maybe earthed fortuitously by other means too.
RCD would trip, if earth is @ Earth potential 😎
You are looking for a figure of resistance greater than 23000 ohms when testing between the metal shed and the true earth (probably taken from a nearby socket).
I would use a multi function tester for this.
My multi meter would also have a continuity reading range which could test it.
Someone with better understanding than me may suggest a different method involving taking voltage readings, but I would not have the confidence to be explaining this.
Thank you HHD, my plan for both tests works be to use an MFT and wander lead between shed and my MET at the board. Flick between continuity setting (looking for a high reading indicating no connection to earth) and then the voltage setting and hopefully get a 0 Volt reading indicating 0 touch voltage potential.
If both tests read in this way I do not require earthing of the shed.
Can somebody confirm my thoughts on this or am I way off? 😅🤦‍♂️
As much as I hate saying this, on this occasion I'm saying get an electrician.
There are all sorts of issues with metal buildings, but consider this one: You nicely isolate your electric accessories from the metal structure and the metal structure itself happens to be isolated from true earth.
Everything is good, everyone is happy.
Over the years the tumble drier has shaken itself to be in contact with the metal structure and at the same time the paint of the tumble drier and metal building have rubbed through so it is in good contact (this part is very normal and common - especially with a washing machine)...
A fault occurs, making the earth of the electrical system live (let's not get into the hows, what's or why's) and now the metal building is live.
My view on this is it would be best if this is a full blown TT system with suitable RCD and a local earth to lock the metal stucture to local true earth.
Additionally my view is the armour of the cable should be totally isolated at the shed, no silly superfluous box, not even a cable gland. Note the voltage between the 2 metal enclosures: 1764714763296.jpeg The problem had been there for a long time and that short piece of plastic conduit was just one of the things specifically added to overcome RCD tripping problems.
and my solution to stop that happening. Ignore the brown/black reversal - I believe that was my error when swapping the RCD [from the house] and main switch [to the house] during faultfinding. 1764714790677.jpeg
Additionally my view is the armour of the cable should be totally isolated at the shed, no silly superfluous box, not even a cable gland. Note the voltage between the 2 metal enclosures: View attachment 124126 The problem had been there for a long time and that short piece of plastic conduit was just one of the things specifically added to overcome RCD tripping problems.
and my solution to stop that happening. Ignore the brown/black reversal - I believe that was my error when swapping the RCD [from the house] and main switch [to the house] during faultfinding. View attachment 124127
I get what you're saying, but with my setup the risk is tiny. Everything I’m using is plastic both in the house and the shed, also separating further by mounting onto wood so there’s no exposed metal on the accessories. I’m also on a TNS supply, so there’s no PME or PEN failure to worry about.
A fault like that would need a lot of things to go wrong at the same time, and someone would have to be touching the shed when it happens. Earthing the SWA at both ends gives me full continuity and a reliable fault path back to the house RCD, which massively reduces the chance of the shed ever floating live.
I thinks it's overkill giving my supply and planned installation.
Worse case I could install a fly lead from the socket onto the shed but I don't think it's necessary.
Making it TT is overkill
What's your view on this westward given everything above? I feel confident installing once tests are done to go ahead with and with my planned method. Are those tests I described correct and is there anything else I need to think about? Very close to my level 2 quals but real world experience is lacking so just want to make sure 👍
The sheds still metal, test for an extraneous part if not carry on😎