TN to TT and having differing earthing systems in close proximity is something completely different. The armour of the supply cable in your example does need earthing for ADS purposes but how this armour is isolated at the TT end needs correct consideration.
Yes that is exacly my meaning.
I was using it as another example of experience rather than trying to saying it applies here, however the metal shed is a classic example of 'which earth?'
Borrowed a MFT from work and tested the shed.
Got reading of more than 2000 Ohms on continuity and 0.1 Volts on potential difference so I have confirmed it is non extraneous 👍
You need to test it but the MFT might not have suitable resolution on IR.
Ran test today but concrete and shed were wet from rain so had a reading of 0.00. tester still shows greater than 2000 when nothing connected. I also repeated continuity and voltage tests and they were repeating the same. High reading for continuity and 0.1 volts.
I'm happy given all the factors and other tests that have been done. Just wondering if you would run an earth fly lead from the new shed socket to the wall of the shed itself as an extra precaution and fault path back to the house RCD?
It’s not extraneous so no bond conductor required, the metal shed requires an earth connection via socket outlet.
This becomes bit of a head scratcher, the obvious scenario would be to make an earth connection, but the actual building is deemed to be isolated from potential Earth, the power point mounted on wooden base. Reality is what happens when a fault on the equipment happens & touching the metal shed or even steps out of the shed onto potential Earth.
Conventional says earth the shed😎
Agreed, earth via a fly lead not bond back to MET 👍
Thanks everyone for the input and advice. Greatly appreciated.
Totally unnecessary.
Westward... you have to expand?
Most people on here know that your knowledge is vast, so we're inclined to listen to it even without thorough explanation, same as with Davesparks (although he usually explains). But a number of people have mentioned about what happens when the metal shed comes into contact with the line conductor, and the person touches the shed, whilst in contact with the earth?
Do let me know your thoughts? I need to understand!
I've explained previously why this shouldn’t be considered an extraneous-conductive-part if it tests to satisfy that. Back to the 15th Ed we lived with "what ifs" and sticking green/yellow wires on any piece of metal that stood still which wasn't the greatest idea in the world. Connecting this shed to the earth of the electrical system could result in it carrying fault current under some conditions so you wouldn't want to be touching it and true earth.
I've explained previously why this shouldn’t be considered an extraneous-conductive-part if it tests to satisfy that. Back to the 15th Ed we lived with "what ifs" and sticking green/yellow wires on any piece of metal that stood still which wasn't the greatest idea in the world. Connecting this shed to the earth of the electrical could result in it carrying fault current under some conditions so you wouldn't want to be touching it and true earth.
True Earth meaning outside of the shed which would be the scenario on most cases externally. At least if connected to the earth of the installation the fault will be cleared by the protective device😎