Ran test today but concrete and shed were wet from rain so had a reading of 0.00. tester still shows greater than 2000 when nothing connected. I also repeated continuity and voltage tests and they were repeating the same. High reading for continuity and 0.1 volts.
I'm happy given all the factors and other tests that have been done. Just wondering if you would run an earth fly lead from the new shed socket to the wall of the shed itself as an extra precaution and fault path back to the house RCD?
Hi Adam.
When giving results you have to give them accurately. This isn't me being picky, it's just how it should be with electrics.
When you say 'had a reading of 0.00', is this an Insulation resistance (IR) test or a continuity test. Also what are you testing between (which 2 points)? Plus I'm assuming ohms?
Also, I didn't realise you were a trainee (apologies if you mentioned this, I missed it).
It's a simple test to test if something is extraneous. You are testing between the suspect object (i.e. your metal shed), and known earth. For known earth I would be using the earth of a socket (using a plug in adaptor, or even better if you have a main earthing terminal that is accessible outside of the consumer unit. Failing that you need to figure out how you can safely find a known earth. If you are 100% confident in removing the lid of the consumer unit and have been shown how to do this properly, then you can get to the earthing bar in there.
You then attach one probe to the shed (on your multi function tester) and the other to the known earth. My Megger goes up to 99.9K ohms on the continuity setting so I would probably use this function, as I am looking for a figure above the magic figure of 23K ohms.
A figure of 23k (23000) ohms or above shows that the item in question is an extraneous conductive part (ECP).
We get this figure of 23K ohms by using Ohms Law (Voltage (V) = Current (A) x resistance (ohms) ) this is commonly shown as V = I x R (I is current in amps)
We know the voltage (230V), and we use a figure of 0.01A for I. We use this figure which is the same as 10milliamps because it is the assumed value for the 'let go threshold'. I.e. If we touch a piece of metal and get 10milliamps through us we 'should' be able to still let go.
Now we can put those 2 figures in to Ohms law to find R.
230 = 0.01 x R
(divide both side by 0.01 (you need to know how to mess around with an equation to get to the figure you want) )
Therefore R = 230 / 0.01 =
23000 ohms (or 23k)
Have a play around with the figure of 10milliamps, make it higher and lower, put the different figures back in to the equation and see how the resistance value changes. This brings greater understanding of what you are actually doing.
Apologies if you already knew this. I enjoy writing out maths, and it's good for me to see this written down every now and then to rejog my memory.