As an adult learner, I have lots of theory but not enough practical experience so I'm hoping I can get some help here (not abuse). I'm trying to get my head round earthing SWA to an outbuilding with no extraneous conductive parts. I understand the problems of exporting a PME supply etc. If I have a 3 core 6mm2 SWA and use one of the cores as the CPC and the house CU has RCD protection why do I need to earth the SWA? My thinking (probably wrong) is that if a spade goes through the cable it will cause a short between phase conductor and earth conductor and trip the RCD?
If the armour is not earthed, and your spade happens to dig into the armour and the live (L, line) only, ... the armour goes live, so does your spade, ... and anyone touching the metal parts.
Thanks for taking the time to reply. Makes perfect sense - why didn't I figure that out!
Reactions: DPG
Reply to Earthing SWA in the DIY Electrical Advice area at ElectriciansForums.net
resitting Saturday my am2 4 sections a3/b/d/e swa and sy failed on protective conductors on both swa i under stand thats the earths i...
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...