varilite
If it looks like tns get ze readings typical of tns then it could be tncs
If it looks like tns get ze readings typical of tns then it could be tncs
LV jointers on a HNC course?
Most LV jointers I’ve come across are on a par with pond life.
Skilled yes, theoretical no. Most of them it takes 10 minutes to think “I’m getting a shock.”
Only on older cable joints, where and when a fault has occured or part of a converting exercise. There are many network cable distributions that haven't been touched since they were installed from the 60's on housing estates and the like!! All cables connected at TX substations have a neutral earth connection, be they TN-S or TNC-S, on TN-S cables, it will be the only place where it's neutral is connected to earth, unless newer jointing has taken place.Whilst what E54 stated is by and large correct, could I also point out that technically all TN-S cables are effectively TN-C-S indirectly because they are stacked wherever a joint is put in
Yes all I meant was as long as disconnection times can be achieved it dosen't matter if its tncs or tnsI know that:
TNS max Ze is 0.8 ohms, and Ze should be different from Ze(L-N)
TNCS max Ze is 0.35 ohms, and Ze should be the same as Ze(L-N)
Is that what you meant Varilite?
Single phase, three phase or both??TNCS max Ze is 0.35 ohms,
Only on older cable joints, where and when a fault has occured or part of a converting exercise. There are many network cable distributions that haven't been touched since they were installed from the 60's on housing estates and the like!! All cables connected at TX substations have a neutral earth connection, be they TN-S or TNC-S, on TN-S cables, it will be the only place where it's neutral is connected to earth, unless newer jointing has taken place.
As you say, most of the UK's LV networks have indeed, been effectively converted to TNC-S but certainly not all of them!!
What we do need to point out here, is there is a very big difference between the terms TNC-S and PME. A cable that has just one or two N-E joint connections along it's path, cannot be deemed as suitable for a PME connection, otherwise virtually every existing TN-S / TT installation could be converted to a PME connection...
Single phase, three phase or both??
each phase to earth for Ze..Sorry, not sure what you mean, always been thought that TNCS is 0.35 ohms, and don’t mater single or 3 phase, just on the 3 phase you measure each phase to earth, that’s all?
=Outspoken;781276]E54, in a few cases there may not be major joints that have been staked, however it is safe to say the street furniture will have been upgraded over the years and this process alone is giving the system effective multiple earths via the metalwork buried in the ground, also for a number of years where the local operators (normally in the Board days but it does happen today) have inserted solid isolation points in the ground, these have always been staked into the surrounding ground, so it is rare, though not impossible, to find a buried supply cable in the UK these days that does not have multiple earth paths and thus should give very low resistance readings.
E54, I think you have fallen into the trap of confusing the origins of the term PME. Originally this was coined by the now defunct London Electricity Board to differentiate a supply from the old single connection types of separated cables (Standard TN-S) from combined N-E type cables that were dedicated to a combined neutral-Earth connection by design.
TN-C-S was never deemed a PME by the LEB because they used the term Protective Multiple Earth to describe any supply cable that had multiple dedicated and deliberate Earth connections along it's supply route. It was later that people began to refer to TN-C-S as PME, which was an incorrect connection because in it's purest form, running from a local sub-station to the street and T-off to homes/businesses it is not actually a PME systems unless it has been multiple spiked.
Most overhead supplies are now deemed PME because at the 11kV Tx on the pole they are spiked into the ground beside the pole, although clearly some are still to do in very rural areas and it is likely wise to assume it is TT unless your DNO specifically states otherwise