Is the link between the neutral and earth terminal in the cut out still in place ?
Must admit, I was wondering if it was fitted, or had ever been fitted.
I think you are assuming too much competence on behalf of the meter fitter!
Probably
As I recall, when I had an isolator fitted, the guy didn't take any measurements at all - only a quick check of polarity.
I thought it was quite obvious that the earth was unconnected, as it isn't a main cable entering the head, just two cores, line and neutral - is it fed from overhead lines, or is there a proper intake head somewhere?
TN-C-S is like that. Just two cores in which may be separate cables overhead, or concentric (buried or overhead). Inside the service head (a.k.a. main fuse unit) the earth terminal is linked to the neutral conductor. Out in the street, there will be multiple points where the neutral is earthed - hence the name "PME" (protective multiple earthing).
As long as the neutral conductor doesn't get broken, this does give a very good earth.
 
Must admit, I was wondering if it was fitted, or had ever been fitted.

Probably
As I recall, when I had an isolator fitted, the guy didn't take any measurements at all - only a quick check of polarity.

TN-C-S is like that. Just two cores in which may be separate cables overhead, or concentric (buried or overhead). Inside the service head (a.k.a. main fuse unit) the earth terminal is linked to the neutral conductor. Out in the street, there will be multiple points where the neutral is earthed - hence the name "PME" (protective multiple earthing).
As long as the neutral conductor doesn't get broken, this does give a very good earth.
But that isn't configured as as a main intake head aka service head, there would naturally be no connection between the neutral and earth connection.

That could be configured for TT, or TN-C-S, but it isn't configured for anything!

So T at best!

Even if it does end up being interconnected for TN-C-S, given the age of the cable it isn't necessarily PME
 
But that isn't configured as as a main intake head aka service head, there would naturally be no connection between the neutral and earth connection.
I think I must have lost track of the thread here.
Looking at the photo posted by Zerax, I can't see whether there's an E-N link installed or not. It's not an area (features of different types of service head) I have much experience with, and the ones I have seen inside don't have the presence or otherwise of the link particularly obvious (if visible at all).

But if TN-C-S, all it would have is two cables (or two cores in one cable), with the N-E link fitted to provide the earth connection. So I don't get your comment that "it's obvious there isn't an earth as there's only two single cables". Our connection at church is "just two cables", and that's PME/TN-C-S - looking at the photos I have, looks distinctly similar to Zerax's photo, two cores in, two cores out, and an earth block on the side (confirmed during a DNO engineer visit to be PME linked).
 
I agree, but think most of us on here where too afraid to question the fact that there is an obvious earth visible. I NEED THE SMILIES BACK.
 

Reply to Earthing system quiz in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, As mentioned, I’ve got what looks like a TNCS system but CPC is coming via an earth rod???? Not tested TNCS system yet to see if earthing...
Replies
9
Views
604
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Went to a house to extend a circuit and upon doing the minor works I couldn't figure the earthing system. There was no DNO cutout and L and N came...
Replies
1
Views
728
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
491
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
667

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock