Hawk

There is a distributors earth and also an earth spike in this installation. Why would this be? Photos attached
 

Attachments

  • IMAG0508.jpg
    IMAG0508.jpg
    94.7 KB · Views: 128
  • IMAG0507.jpg
    IMAG0507.jpg
    105.8 KB · Views: 119
probably was TT and then converted to pme. earth rod left in. nowt to worry about.
 
Your first picture certainly looks like a TNC-S system, and I guess that your second is trying to show the earth rod side of things, but it's not clear, well to me at least.

It looks like an industrial/commercial installation so there maybe reasons for what you have

1) Originally TT but converted to TNC-S and could not be chewed to remove
2) Out lieing building originally not now in use
3) Functional earth for IT or such like equipment
4) Agi or some such type of installation
 
It is a commercial premises. There is an earth spike outside the building which the owner says was installed when the installation was done. Would it be to get a lower Ze?
 
Well if it is TNC-S not sure the extra rod would bring it down much lower, unless it is a DNO spike but if it was it wouldn't go into the installation.

Another one of life's mysteries, no sign of a lightning protection system???
 
Incase the neutral drops out which would leave you with a live and no earth, very bad situation
 
an earth rod would never reduce the Ze of a TNC-s earthing system, unless you banged one in to australia! LOL. basically a dinosaur back up to technology if technology fails ( lost N).
 
All PME/TNC-S supplies should have a local earth rod connected to the MET. Standard practice on the Continent. Mind, it would be totally useless if you apply the 200 ohm max, to which UK TT systems is now based!! Look at the earth rod being a local N-E link on the PME/TNC-S supply!!!
 
It is a commercial premises. There is an earth spike outside the building which the owner says was installed when the installation was done. Would it be to get a lower Ze?

May have been a temporary TT system spike until the TN-C-S was installed by the DNO, then DNO turn up to convert the head and did not remove the spike the lazy gits
 
May have been a temporary TT system spike until the TN-C-S was installed by the DNO, then DNO turn up to convert the head and did not remove the spike the lazy gits

No, in fact sensible, ''if'' they tested the Rod and found a decent Ra value!!
 