HappyHippyDad

-
Esteemed
Arms
Supporter
A customer has asked me to fit an easee one EVCP. I notice that it has a type B RCD in it (I think). We are not supposed to fit a 'lower grade' RCD upstream, due to the blinding effects.

Its not possible (at least not easily) to fit a type B RCBO into the 'fusebox' branded consumer unit, so I am unsure how to proceed?

I feel I may be missing something here as there must be 1000's of easee one EVCP's fitted?
 
No it would mean the inbuilt RCD protection is not compliant with BS7671 and the CoP.
A lot of the early charger points had built in RCDs with did not satisfy EN 61008 and hence did not comply to the standards. If it does comply is RCD protection upstream necessary?
 
No it would mean the inbuilt RCD protection is not compliant with BS7671 and the CoP.
A lot of the early charger points had built in RCDs with did not satisfy EN 61008 and hence did not comply to the standards. If it does comply is RCD protection upstream necessary?
The route is through the ceiling, all the way to the outside (from consumer unit). Then in conduit to the EVCP.
It's PME, so has fault protection from ADS.
I do get a little confused about what 'doesn't' need to be RCD protected.
 
Its not possible (at least not easily) to fit a type B RCBO into the 'fusebox' branded consumer unit
If you have 3 spare ways in the board, you could potentially do what I did for a heat pump circuit I worked on recently. I shortened the busbar by two modules, installed the type B RCCB in the space, and installed the circuit MCB next to it on the last 'tooth' of the busbar. The MCB fed the RCCB which then fed the circuit.

This was with fusebox gear btw.
 
Google AI declares the Easee RCD as being compliant with BS610081 etc, but no references.
Not being convinced, I had a further look, which revealed this... does it help?

In summary:
IMG_0004.jpeg
 
Last edited:
Crikey, so is my only option here to take up 3 ways in the consumer unit. A type B RCCB (2 ways) fed by an MCB?

I think I may try and persuade them to buy a different unit!
 
#7 indicates the built in RCDs satisfy the standards so an upstream RCD would not be required but I would double check your unit with the supplier.
Why do you think an upstream RCD is needed?
 
The route is through the ceiling, all the way to the outside (from consumer unit). Then in conduit to the EVCP.
It's PME, so has fault protection from ADS.
I do get a little confused about what 'doesn't' need to be RCD protected.

What type of cable and is it buried in the wall less than 50mm deep at any point?

RCD protection is not required for fault protection in this case, it's not a domestic lighting circuit and presumably the charger isn't in a bathroom so those aren't relevant.

The requirement for RCD protection of the outlet is covered by the unit itself.
 
Google AI declares the Easee RCD as being compliant with BS610081 etc, but no references.
Not being convinced, I had a further look, which revealed this... does it help?

In summary:
View attachment 122421
Don't forget they faced a sales ban in Sweden and their native Norway for lying about the nature of this "RCD". You definitely need to install one. It absolutely and categorically is not a BS EN 61008 or BS EN 61009 device in the EVSE.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
-
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Easee one EVCP has a type B RCD fitted in it.....
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
11

Thread Tags

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
Risteard,
Replies
11
Views
172

Advert

Back
Top