OK, you are completing an EIC, so you are installing this?
You should be well aware that an RCD does not have over current protection, only earth fault protection.
The RCD will NOT trip if the current exceeds 40A, it is only rated to take a total current of 40A, like cooker switches are rated to 45A but will not trip!
If they had over current protection why would there be RCBOs?
You need over current protection for that supply cable.