Hi looking for some advice, basically have an upfront 100mA RCD at 1 DB that feeds another DB with no RCD just MCBs in 2nd DB, now on schedule of tests it says over current which at 2nd DB which will be my 100mA RCD and Associated RCD but where Operating current for each circuit is would you put the 100mA in there too?
 
An RCCB is not an overcurrent protective device. It offers residual current protection (earth leakage) but does not protect against overcurrent. The type of RCD which has integral overcurrent protection is an RCBO.
What Risteard said, what's with this 5 words message?
 
your overcurrent protection for DB2 is the 80A MCB in DB1. for each circuit in DB2, the MCB for the circuit is the OCPD for that circuit alone. bet yo have a few C2's for no 30mA RCD/s
 
your overcurrent protection for DB2 is the 80A MCB in DB1. for each circuit in DB2, the MCB for the circuit is the OCPD for that circuit alone. bet yo have a few C2's for no 30mA RCD/s
Yes then the associated RCD would be the 100mA RCD, what I mean is none of the circuits have RCD so could you put the 100mA in Operating mA for all circuits? It’s failed anyway but person at work says yes but I’m not sure as in a way they still are governed by that upfront RCD
 
see what you mean. enter the 100mA RCD as 100mA and the time/s in the appropriate column.
 

Reply to EICR help in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock