If its an swa feed the obvious question would be are the tails ccc suitably rated and does the other cu still meet max zs requirements of the OCPD. One time i would C2 this if its done on the main switch off a consumer unit tailed directly into meter therefore loosing your single point of isolation to the installation. I see no issue with the cables pushed into the double screwed terminal aslong no cores have been loped off to get them in.