hi guys

have my assessment coming up next month. have a question about the minimum mcb rating for an A3 radial (from outbuilding cu). Now the radial has one db socket and one single external socket. the radial has a very low loading (2kw max/9A). now i dont want to to be pulled up for using the wrong MCB. now usually i would just use a 20A mcb as stated in OSG for an A3 radial. problem is the garage has a buried 2.5mm (20A) supply fed from a RCD protected 20Amcb which i would like to utilise. so my question is would a 16Amcb for the A3 radial be acceptable due to the known low loading and the adequate protection offered by the 16Amcb. or has it got to be a 20Amcb as per OSG for an A3 radial with multiple socket outlets. As this is for assessment do you think it nessacary to supply via 6mm/32Amcb to allow for the 20A A3 radial and allow for discrimination?
 
No mate the OSG is a guide and so if you as the designer feels that a 2.5mm radial is best served by a 16amp MCB then there is no problem with that.
 
so as long as i can explain to my assessor my reasoning for selecting the 16AMCB then there should be no problem?
 
No that should be fine. If your using an existing cable emphasise the fact that you tested it to make sure it was ok and point out the IR results.
 