I have an electrical installation in a garage. The supply from the house to the garage is protected by a 80 Amp 100mA RCD.

When I use certain tools in the garage, mainly an orbital sander and a finger grinder the main RCD in the house trips and plunges the place into darkness, seemingly by passing the local MCBs in the distribution board in the garage. The ring is protected by a Wylex B32 NSB breaker.

The tools in question seem to operate for a short period of time but after say 5/10 minutes they trip the RCD each and every time until I have to stop using them.

I assume they are not faulty as they work in the house for unlimited amount of time.

Do I need to change the type of MCBs in the local board for something more or less sensitive, with a view to the local protection operating, or is this giving to give me further nuisance tripping?

I changed the RCD in the house recently from a 30mA unit to the 100mA and I still have the same problem..
 
I have an electrical installation in a garage. The supply from the house to the garage is protected by a 80 Amp 100mA RCD.

When I use certain tools in the garage, mainly an orbital sander and a finger grinder the main RCD in the house trips and plunges the place into darkness, seemingly by passing the local MCBs in the distribution board in the garage. The ring is protected by a Wylex B32 NSB breaker.

The tools in question seem to operate for a short period of time but after say 5/10 minutes they trip the RCD each and every time until I have to stop using them.

I assume they are not faulty as they work in the house for unlimited amount of time.

Do I need to change the type of MCBs in the local board for something more or less sensitive, with a view to the local protection operating, or is this giving to give me further nuisance tripping?

I changed the RCD in the house recently from a 30mA unit to the 100mA and I still have the same problem..
There is an earth fault on either one of your tools or the associated wiring, an RCD trips when there is a inbalance, ie a fault to earth, and an RCD does not provide overload protection, it isn't bypassing the CBs it only doing its' job in protecting you from a dangerous fault, don't swap anything, get an electrician to test the wiring and the tools used there. To help you could check the Tools for damage to the flexes, plugtops etc, but lt sounds like one of your tools is working OK when it's coo; but as you use it, it heats up and expansion causes the innards to expand and produce the fault that trips the RCD.
 
Last edited:
I take it the 80A 100mA RCD serves both the house and the garage. A RCD works by sensing an imbalance between live and neutral hence why the MCB's don't trip. I wouldn't assume that the tools are good just because they work somewhere else unless they have been properly tested. Why on earth did you change a 30mA unit to a 100mA unit? Doing that has put you and anyone else at greater risk as 100mA RCD's are not made to provide additional protection required for socket outlets etc.
 
As per Pete above there is probably a latent fault, quite possibly a neutral-earth fault on one of the garage circuits. The fault may be there all the time but it only passes enough current to trip the house RCD when the load of one or more power tools is present within the garage, hence the tools work OK in the house. Electrical testing on the garage circuits and submain would be my next step.

Also as above, re-fit the 30mA RCD in the house. The 100mA does not provide protection against shock, so you have downgraded your installation to non-compliance.
 
as above, but also note that it would be better to feed the garage from a non-RCD circuit and then firt a 30mA RCD in the garage. then it would trip in the garage, not the house. this assumes that the feed from the house does not require RCD protection in itself.
 
Hi - agree with Folks above, there’s a fault to be found. Please you need to restore the 30mA RCD for the house as you’ve now made the installation non compliant and removed a safety net. With a fault known to be present ... oh dear!
 
Are both the sander and grinder in the garage being used in an extension lead or directly in a 13amp socket?
Are they always plugged in the same socket?
 

Reply to Electrical Discrimination Issues in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K
Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock