Quick question for my instal cert; would a SELV fan powered from the local lighting circuit be classed as electrically separated if it is ran through the step down transformer (230-12v) and not carrying the earth through?

Thanks.
 
Cheers for the reply. From what i remembered from college the primary and secondary windings on the transformer dont physically meet and theres no earth carried through in this instance so its completely separated. The nic bloke who reviewed my test cert said electrical separation only applied to shaver sockets and not selv fans so just wanted to double check as he made me doubt myself. Maybe he was just having a bad day?
 
Its to do with the relationship to earth.
As mentioned, shaver point, no voltage when checked from either pole to earth,
Same with a 230/230 portable transformer, the blue ones. 230 out but nothing to earth.
Pelv you will find 12v to the earthed negative.
Selv is nothing to earth.


Boydy
 
Last edited by a moderator:
If it has the symbol of a square in a square it's double insulated, same thing really, no earth required and if a fault occurred no chance of contact with any live parts
 