kristian

so i got called out to fix a emergency light in the mens toilets at a betting shop.

was a 2d lamp type fitting. the manager had already changed the lamp.
i put my voltage stick on it and there was power both from the permanent live and the switched live but no juice comin out the lamp. for some reason when i removed the neutral the lamp came on in emergency mode...very dim.

i asked to see the key switch but he had no key for it and mine was in the other van. so i said id have to come back

ive left him with just a normal fittin so at least he has some light in the toilet but this obviously wouldnt comply with regs.

so does the fault lie in the key switch if theres power on both live supplies.
 
Sounds like the batteries have had it kristian, when you disconnected the neutral you simulated a mains failure and the light came on - as it should.
 
i assumed it was the batteries or control gear to start so i replaced it with a new fitting and still had no luck so had to put the normal fitting on
 
wouldn't be a key switch problem if you have live at the fitting. sounds like neutral is ok too (unless there are 2 neutral terminals if the fitting incorporates a pir, and the neutral terminals haven't been linked) sounds like lamp is ok as it comes on when neutral lost. maybe you were given another dodgy fitting?
 
na theres no pir. its switched from the managers office. there voltage goin into the control gear, how can i tell if its comin out? i have a multi meter but never used it. im new to this fault finding business
 
Are you saying you do not know how to use the multimeter? You need to set it to ac volts and check for 230v on the switched live and 230v on the perminant live. It sounds like the light is not working in normal use, but is in emergency mode. What way did you connect the ordinary light? Did you use the switched or perminant live to get it to work.
 
for the new fitting iliterally disconnected the old fitting and then replaced it for the new one, everything in the fitting was already wired up.

no havent used the multimeter before. never had to dring my apprenticeship. its bad i know!
to connect the normal light i removed the permanent live and left it off the switched live
 
haha. no worries. mate. dont think a drawin would do me anygood any ways its only the 2 lives, neutral and earth goin it to the unit. the rest comes pre wired. ill test the control gear on it tomorrow.

thanks for lookin though
 
It will all look different tomorrow.
Most Emergency lights come with a flying lead disconnected so the batteries don't go flat in transit?
 