Discuss Enclosure used as earth in the Industrial Electrician Talk area at ElectriciansForums.net

Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:   American Electrical Advice Forum

Reaction score
34
Hi all, question regarding earthing in hazardous areas distribution panels. The issue is that on most equipment in hazardous areas they use the metal of the enclosure as the earth so if a threaded entry and metal enclosure no need for internal earth cable, like wise if going through a clearance hole they would put serrated washers on the inside given the earth through the enclosure. Now have came across this in a distribution board where the entry is threaded, the enclosure is metal but the issue I’m having it’s a removal gland plate that the gland is threaded into then is bolted inside the enclosure but there is a gasket between the gland plate and dist board. It’s getting metal to metal contact with six 10mm bolts holding it in place but on this dist board there is earth terminals to terminate but the cable feeding the dist board is 70mm going into main isolated and the din rail earth terminals are 16mm. So they have taking a 16mm earth from the gland plate to this earth terminal. Now this is only 300mm if that, of 16mm earth to the gland plate. My question is will 300mm if 16mm earth cable carry fault current for that short run for a 70mm cable as a 35mm earth cable won’t fit into terminals without going to manufacture to get permission to replace with 35mm earth terminals as this is a EXe. Mostly inside the dist board they are using the enclosure as the earth with earth din rails terminals onto din rail then out going cables but nothing at the other end. Sorry for the long winded story. Thanks in advance.
 
As you already recognise, as your line conductor is 70mm then 35 mm would automatically satisfy the protective conductor sizing requirement of Table 54.7

16mm may well be adequate but this will need to be confirmed by using the adiabatic equation. Will need some more info for this though.

What is the PEFC at this enclosure and what is the details of the OCPD that is protecting it?
 
. My question is will 300mm if 16mm earth cable carry fault current for that short run for a 70mm cable as a 35mm earth cable won’t fit into terminals

Have you calculated the size of cpc required? Unless there are special rules affecting this 35mm would usually be bigger than actually needed.
 
The OP hasn't been seen since he posted this in May.
 

Reply to Enclosure used as earth in the Industrial Electrician Talk area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock