Im a sparky but have dropped my NAPIT registration, a tenant of mine asked to install an EV charger and asked me to install it, I said I could not because I am no longer NAPIT registered, they got another installer to intall.

So I had previously (When I had NAPIT registration) installed a 10mm SWA from the main consumer unit to the garage on a 45A MCB that goes to a sub board, as part of this to be EV ready I ran a sheilded cat 6 cable along with the SWA..

The tenant has sent me a photo of the install of the ohme pro home EV charger, however I noticed the cat6 cable still coiled up in the garage, reading online it seems the ohme pro home EV charger only has one CT clamp (With no option to add a second which seems silly), the house is a large 4 bed house with electric shower and I know the cutout has only a 60A fuse.

I am guessing the installer only put the CT clamp on the sub board to ensure that this does not go above 45A.. I don't install EV chargers but my thinking when I ran the cat 6 cable was the EV charger would need a CT clamp at the sub board, to limit that to 45A and then another to the cutout to limit that to 60A...

Could anyone who knows about EV charger installs tell me if this is correct. I think maybe the tenant needs a different EV charger..
 
Im a sparky but have dropped my NAPIT registration, a tenant of mine asked to install an EV charger and asked me to install it, I said I could not because I am no longer NAPIT registered, they got another installer to intall.

So I had previously (When I had NAPIT registration) installed a 10mm SWA from the main consumer unit to the garage on a 45A MCB that goes to a sub board, as part of this to be EV ready I ran a sheilded cat 6 cable along with the SWA..

The tenant has sent me a photo of the install of the ohme pro home EV charger, however I noticed the cat6 cable still coiled up in the garage, reading online it seems the ohme pro home EV charger only has one CT clamp (With no option to add a second which seems silly), the house is a large 4 bed house with electric shower and I know the cutout has only a 60A fuse.

I am guessing the installer only put the CT clamp on the sub board to ensure that this does not go above 45A.. I don't install EV chargers but my thinking when I ran the cat 6 cable was the EV charger would need a CT clamp at the sub board, to limit that to 45A and then another to the cutout to limit that to 60A...

Could anyone who knows about EV charger installs tell me if this is correct. I think maybe the tenant needs a different EV charger..
I would have questioned putting in a 45A supply to a garage consumer unit on a large 4 bed house with a 60A cut out I would have thought that would have required at least up rating to 80A minimum and realistically 100A. That said I don't know the MD for the property. I would guess there is no Electric cooker? EDIT see there is a an Electric Shower.

The application to the DNO should have stated MD and on a 60A supply it would require curtailment.

The CT has to go on the main intake that is the only way to protect the main cut out from overload.

The garage sub board will be protected from overload by its own protective device.

I am hoping the 45A supply was put in due to the future EV charger in which case it should have been sized appropriately. In other words the 45A supply should be adequate for the loads it was designed for. If there are other heavy loads in that garage then the EV should have been supplied separately to avoid the garage CU from being overloaded.
 
Last edited:
Upvote 0
I would have questioned putting in a 45A supply to a garage consumer unit on a large 4 bed house with a 60A cut out I would have thought that would have required at least up rating to 80A minimum and realistically 100A. That said I don't know the MD for the property. I would guess there is no Electric cooker? EDIT see there is a an Electric Shower.

The application to the DNO should have stated MD and on a 60A supply it would require curtailment.

The CT has to go on the main intake that is the only way to protect the main cut out from overload.

The garage sub board will be protected from overload by its own protective device.

I am hoping the 45A supply was put in due to the future EV charger in which case it should have been sized appropriately. In other words the 45A supply should be adequate for the loads it was designed for. If there are other heavy loads in that garage then the EV should have been supplied separately to avoid the garage CU from being overloaded.

Thanks,

Yes the 10mm SWA was replacing a 1.5mm micc cable, there is only a double socket, a socket for the electric garage door and a couple of lights in the garage so the load is not going to be high, the current carrying capacity of the 10mm SWA is around 70A ad buried underground so the 45A breaker could be upgraded if needed however like you say is protected.. The cable was sized to future proof for an EV charger.

When I changed the main consumer unit (including full rewire) about 6yrs ago I tried to get the DNO to upgrade the 60A fuse due to the MD being higher but being the DNO they refused and said if it did ever blow I have permission from the head of the area who came out to the property to upgrade to 80A..

The charger they installed is prewired and only has one CT clamp, my idea was if the charger installed had two CT clamps put one on the garage CU at 45A, and the other at the main incomer at 60A (80A if you could upgrade the fuse).

Because the cat 6 I installed is still coiled up I know the CT clamp does not go back to the main incomer so either there is no CT clamp or their is a CT clamp on the garage consumer unit, they have given the MD of the house as 44A which is a complete load of rubbish considering an EV charger and an 11kw electric shower is in the house.

My thinking is the best way to make it comply is use the cat 6 to take the CT clamp back to the main supply and limit that to 45A, that way it would stop the MCB to the garage overloading and would stop the main fuse blowing.. I am concerned because I know it will be Christmas day when the car is on charge, electric oven and hob going, then someone jumps in the shower and someone else puts on the kettle and the main fuse will blow and they will call me as the landlord..
 
Upvote 0
Yes the 10mm SWA was replacing a 1.5mm micc cable, there is only a double socket, a socket for the electric garage door and a couple of lights in the garage so the load is not going to be high, the current carrying capacity of the 10mm SWA is around 70A ad buried underground so the 45A breaker could be upgraded if needed however like you say is protected.. The cable was sized to future proof for an EV charger.

That was what I was checking. In that instance there is no need to worry about the garage supply being overloaded even if the charger is at max.
When I changed the main consumer unit (including full rewire) about 6yrs ago I tried to get the DNO to upgrade the 60A fuse due to the MD being higher but being the DNO they refused and said if it did ever blow I have permission from the head of the area who came out to the property to upgrade to 80A..
Normally they will upgrade to 80A no fuss no charge as it doesn't normally require any work other than replacing the fuse. I can only assume there are some infrastructure problems for them to refuse.
The charger they installed is prewired and only has one CT clamp, my idea was if the charger installed had two CT clamps put one on the garage CU at 45A, and the other at the main incomer at 60A (80A if you could upgrade the fuse).

Zappis can have up to 3 CT's but not sure they do curtailment at more than one supply point though? Normally the extra CT clamps are used for Solar diversion to prevent grid usage when excess solar is available or monitoring.
Because the cat 6 I installed is still coiled up I know the CT clamp does not go back to the main incomer so either there is no CT clamp or their is a CT clamp on the garage consumer unit, they have given the MD of the house as 44A which is a complete load of rubbish considering an EV charger and an 11kw electric shower is in the house.
That's naughty DNO have approved this thinking its ok when even without the EV charger the MD must be exceeding the supply at times.
My thinking is the best way to make it comply is use the cat 6 to take the CT clamp back to the main supply and limit that to 45A, that way it would stop the MCB to the garage overloading and would stop the main fuse blowing.. I

You seem concerned the garage will be overloaded but cannot see that if there is just a double socket an electric door and lights. Of course you can do this and if they charge mainly overnight then it won't affect charging. There could be an issue during the day though, they won't get the most they could get out of the charger if other loads kick in.

You should really set the curtailment to the cut out rating, I believe that EV chargers reduce the charging rate whilst approaching that limit and not at that limit.

But yes the CT clamp must go back to the main supply probably would say do that as a matter of urgency. With negligible loads in the garage you have effectively no curtailment in operation.
am concerned because I know it will be Christmas day when the car is on charge, electric oven and hob going, then someone jumps in the shower and someone else puts on the kettle and the main fuse will blow and they will call me as the landlord..

Absolutely.
 
Upvote 0
That was what I was checking. In that instance there is no need to worry about the garage supply being overloaded even if the charger is at max.

Normally they will upgrade to 80A no fuss no charge as it doesn't normally require any work other than replacing the fuse. I can only assume there are some infrastructure problems for them to refuse.


Zappis can have up to 3 CT's but not sure they do curtailment at more than one supply point though? Normally the extra CT clamps are used for Solar diversion to prevent grid usage when excess solar is available or monitoring.

That's naughty DNO have approved this thinking its ok when even without the EV charger the MD must be exceeding the supply at times.


You seem concerned the garage will be overloaded but cannot see that if there is just a double socket an electric door and lights. Of course you can do this and if they charge mainly overnight then it won't affect charging. There could be an issue during the day though, they won't get the most they could get out of the charger if other loads kick in.

You should really set the curtailment to the cut out rating, I believe that EV chargers reduce the charging rate whilst approaching that limit and not at that limit.

But yes the CT clamp must go back to the main supply probably would say do that as a matter of urgency. With negligible loads in the garage you have effectively no curtailment in operation.


Absolutely.


Thanks for the reply, I think you are correct I should not worry too much about loads in the garage, the sockets are on a 16A supply and lights are on a 6A, but in reality the lights are nothing much and the sockets plus the charger would not be able to overload the 45A mcb before overloading their own RCBO..

So I think setting the CT at the cutout to the size of the fuse makes a lot of sense, I have just spoken to the low carbon team at national grid and the installer has not informed them that an EV charger has been installed.

I have emailed the installer with my concerns so will see what they come back with, honestly the cable has gone at a diagonal from the DB it looks dog rough but ultimately functional, just not how I would ever install anything. At the moment I don't know if they even fitted any CT clamp, its frustrating as hell cause I know I can do a better job but because I am basically retired I have dropped my NAPIT certification as it was costing too much and I was not doing enough notifiable jobs but this guy can do that sort of rubbish job but I can't do a decent job, just shows how messed up the CPS schemes have become..

If I don't hear anything from the installer I will raise it with NICEIC, it does seem at least from my experience that NICEIC installers seem to be worse than NAPIT, but could just be my experience.

Thanks for your help, you confirmed what I thought, always good to get a second opinion...
 
Upvote 0
Thanks for the reply, I think you are correct I should not worry too much about loads in the garage, the sockets are on a 16A supply and lights are on a 6A, but in reality the lights are nothing much and the sockets plus the charger would not be able to overload the 45A mcb before overloading their own RCBO..

So I think setting the CT at the cutout to the size of the fuse makes a lot of sense, I have just spoken to the low carbon team at national grid and the installer has not informed them that an EV charger has been installed.

That is bad they should know that is a requirement. This might open up a can of worms now though. DNO are highly likely to refuse given they refused an earlier request for an upgrade. The hope is that was 6 years ago and things might have changed with regard to an upgrade. Again I assume there are infrastructure issues at that location.

I had an idea they either lied about the MD or didn't submit the DNO application, cannot see the DNO approving an EV Charger on a 60A supply with a realistic MD supplied with a large house with those loads on it.

I guess the only saving grace is you get that 80A upgrade if the main fuse goes! But not really the way you want to get it!

I have emailed the installer with my concerns so will see what they come back with, honestly the cable has gone at a diagonal from the DB it looks dog rough but ultimately functional, just not how I would ever install anything. At the moment I don't know if they even fitted any CT clamp, its frustrating as hell cause I know I can do a better job but because I am basically retired I have dropped my NAPIT certification as it was costing too much and I was not doing enough notifiable jobs but this guy can do that sort of rubbish job but I can't do a decent job, just shows how messed up the CPS schemes have become..

Don't start me on that ...
If I don't hear anything from the installer I will raise it with NICEIC, it does seem at least from my experience that NICEIC installers seem to be worse than NAPIT, but could just be my experience.

There are more NICEIC members than NAPIT members but I know what you mean.
Thanks for your help, you confirmed what I thought, always good to get a second opinion...
You are welcome
 
Upvote 0
That is bad they should know that is a requirement. This might open up a can of worms now though. DNO are highly likely to refuse given they refused an earlier request for an upgrade. The hope is that was 6 years ago and things might have changed with regard to an upgrade. Again I assume there are infrastructure issues at that location.

I had an idea they either lied about the MD or didn't submit the DNO application, cannot see the DNO approving an EV Charger on a 60A supply with a realistic MD supplied with a large house with those loads on it.

I guess the only saving grace is you get that 80A upgrade if the main fuse goes! But not really the way you want to get it!



Don't start me on that ...


There are more NICEIC members than NAPIT members but I know what you mean.

You are welcome


Thanks, they didnt refuse the upgrade 6yrs ago just the guy didn't think it would be a problem so no point but said if the main fuse ever did blow and it was a problem then they are happy to stick in an 80A fuse so don't think there are any infrastructure issues.. After speaking to the DNO they are happy to upgrade to 80A but they need to be informed by the installer..

Could be the installer just forgot but hopefully an email will be the nudge they need.. :)

I hate when people un-necessarily neg on other electricians work but I have had two EV chargers installed in tenanted properties and both have been a problem, first POD point wanted to put a cu in the meter cupboard which I refused saying they can put an mcb in the main cu and then a cu next to that, they apparently would not touch the current install so I installed one for them, then they refused to fit an SPD until I got NICEIC involved who told them yes they needed too..

For most landlords they just have to rely that the person they use is decent enough im thankful at least I have some knowledge of electrics plus other building things that mean I can generally spot a bad job...
 
Upvote 0
Just an update as nobody ever gives an update..

The installer finally got back to me he agreed to go back and move CT clamp to the main tails in the house with the provided CAT6, silicone up hole, put in compression gland, change RCBO to a 40A RCBO as per manual...

Just for reference for the following, I asked him specifically to put the CT clamp on the main tails and specifically asked him if the RCBO he fitted was a double pole RCBO. I also specifically asked that he make sure the charger was setup correctly.

About a week ago the installer went back and made the changes... Today I get a message from tenants the consumer unit is buzzing when the electric shower is on.. Apparently a buzzing came from consumer unit when the EV charger installer was there and he said he sorted it and it seemed to stop.. Obviously worried I go round sure enough a buzzing, thinking maybe its a loose connection. When I open the consumer unit I see the shower live has been moved and the CT clamp is around the shower live conductor, I find the live in the mcb of the shower is a bit loose, thinking this was the buzzing I tighten, move the CT clamp to the main tails.. However when I test I find the CT clamp is the thing causing the buzzing.

So my suspicion is the installer dropped the CT clamp causing it to have issues, and to solve the buzzing moved the CT clamp onto the shower. I called Ohme who have raised a ticket and hopefully they can send out a new CT clamp (I did make sure it was securely closed etc but thinking it can only really be the CT clamp vibrating). Ohme also said the load balance was enabled but was set to 100A, turns out at some point the head was replaced and is not 60A as I thought but is 80A, but should still be set on the charger to 80A load curtailment not 100A, Ohme were really good and said he we sent a photo they could change this setting..

I checked the consumer unit in the garage and my spidey senses tingled when I saw what looked like an older fusebox RCBO, after checked yep its a single pole RCBO..

Honestly ive given up with the installer and will just fix it myself, hopefully a new CT clamp should fix the buzzing and changing the single pole RCBO to a double pole RCBO will get it to a compliant state... I really don't understand how the donut of an installer can get this so wrong, he clearly did not understand what I was saying..
 
Upvote 0
FINAL UPDATE:

So today I went and replaced the buzzing CT clamp with a new CT clamp, the new one also buzzed.. I found in the ohme app that it shows the Amps reading of the CT clamp, this was 0A, even if I turned on the 11kw shower. Even when I disconnect the CT clamp from the cable it buzzed but not as loud.

I moved the CT clamp to the garage and put it round the socket circuit and turned on a kettle in the garage it was getting a correct reading on the charger and not buzzing.

I then checked the continuity of the buried CAT6 cable, and found that there was no continuity, so I went to try a different pair but to do that I needed to strip back the outer sheath and found that the installer had managed to cut through one of the used pair conductors, it looked ok before I cut back the sheath further but must have been hanging on by something, after testing continuity again I got a good reading. I put it all back together and now the charger can see the reading and the CT clamp is not buzzing..

So if you ever get a buzzing CT clamp check the charger can actually get a reading and check the continuity of the ethernet or whatever cable is being used.

Thanks for the help..
 
Upvote 0
Just an update as nobody ever gives an update..

The installer finally got back to me he agreed to go back and move CT clamp to the main tails in the house with the provided CAT6, silicone up hole, put in compression gland, change RCBO to a 40A RCBO as per manual...

Just for reference for the following, I asked him specifically to put the CT clamp on the main tails and specifically asked him if the RCBO he fitted was a double pole RCBO. I also specifically asked that he make sure the charger was setup correctly.

About a week ago the installer went back and made the changes... Today I get a message from tenants the consumer unit is buzzing when the electric shower is on.. Apparently a buzzing came from consumer unit when the EV charger installer was there and he said he sorted it and it seemed to stop.. Obviously worried I go round sure enough a buzzing, thinking maybe its a loose connection. When I open the consumer unit I see the shower live has been moved and the CT clamp is around the shower live conductor, I find the live in the mcb of the shower is a bit loose, thinking this was the buzzing I tighten, move the CT clamp to the main tails.. However when I test I find the CT clamp is the thing causing the buzzing.

So my suspicion is the installer dropped the CT clamp causing it to have issues, and to solve the buzzing moved the CT clamp onto the shower. I called Ohme who have raised a ticket and hopefully they can send out a new CT clamp (I did make sure it was securely closed etc but thinking it can only really be the CT clamp vibrating). Ohme also said the load balance was enabled but was set to 100A, turns out at some point the head was replaced and is not 60A as I thought but is 80A, but should still be set on the charger to 80A load curtailment not 100A, Ohme were really good and said he we sent a photo they could change this setting..

I checked the consumer unit in the garage and my spidey senses tingled when I saw what looked like an older fusebox RCBO, after checked yep its a single pole RCBO..

Honestly ive given up with the installer and will just fix it myself, hopefully a new CT clamp should fix the buzzing and changing the single pole RCBO to a double pole RCBO will get it to a compliant state... I really don't understand how the donut of an installer can get this so wrong, he clearly did not understand what I was saying..
It would be worth replacing the data cable as it has obviously been damaged, and may be unwise to assume that the other pairs are fine/unaffected.
 