Problems with car park lighting columns,fault on circuit.swa cables not connected at light positions,right botched job,some where are undergroung joints,any ideas on how to find them,without digging the whole car park up.
 
depends on the fault. if it's a short, measure the resistance from each end, then calculate the length to the fault, using mOhms/m for that particular cable. if it's open circuit, you're fooked.
 
if you tap ground with hammer you'll get an echo back where jb is.. :)

what at is the actual fault ..
 
which planet are you on today. bloody echo. that's a local scouser news rag.
 
Iwas trying too hard , should if said hollow..

anyhow if it's posts it could be in duct wip it out..
 
if you tap ground with hammer you'll get an echo back where jb is.. :)

what at is the actual fault ..

dead short on both L & n to earth,mayb can get a fault tracer tool,elect boards inject a voltage then find the thumping sound where the fault is,sounds easy ,but I don't think so
 
so measure the R from L to N, with a low ohm meter. then calculate the length to the fault. ssssiimplesss.
 
First have a look around to see if the tarmac has been disturbed by excavation or someone bolting something into the tarmac.
 