davelerave

if (for arguments sake)you're exporting PME with a swa submain-not converting to TT


can the 'main bond' be used as 'cpc' or should they be separate

should the main bond be at least minimum csa required and kept to less than 0.05ohms


thanks
 
Where a circuit protective conductor also acts as a bonding conductor, the requirements for both functions will have to be met.

Also remember that the sizing of the bonding conductor on PME systems is based on the SUPPLY neutral CSA, not the distribution circuit neutral.
 
yes i'm aware of the basic sizing requirement -i'm referring to longer runs

what does first line of your post mean exactly?
 
yes i'm aware of the basic sizing requirement -i'm referring to longer runs

what does first line of your post mean exactly?

It just means that as well as meeting the requirements of regulation 543.1.1 for a circuit protective conductor, it must also meet the requirements of regulation --- (can't remember whatever replaced 547.02.01)
 
For the amount of times this question is asked im wondering if we claim back VAT for it!
 
It just means that as well as meeting the requirements of regulation 543.1.1 for a circuit protective conductor, it must also meet the requirements of regulation --- (can't remember whatever replaced 547.02.01)


one conductor will do both but it must be minimum size required for either(usually the main bond)

is that what you're saying ?

max resistance of main bond is 0.05 ohms?
 
one conductor will do both but it must be minimum size required for either(usually the main bond)

is that what you're saying ?

max resistance of main bond is 0.05 ohms?

That's about the size of it!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
exporting pme
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
6

Thread Tags

Advert

Thread statistics

Created
davelerave,
Last reply from
IQ Electrical,
Replies
6
Views
1,655

Advert

Back
Top