I thought that under the floorboards was deemed as not accessible??
GLENNSPARK your post 16 says "if...and i say if you are going to joint the cable under the floorboard then at least create a proper access hatch for it...
and make its wereabouts known on the dis-board schedule..."
This is still classed as not accessible, isnt it? I thought that all connections done under floorboards had to be maintenance free. Or have I just read the post wrong ... again...
If there was a proper hatch which was documented, then a joint can be made without being MF. Unfortunately, in the real world, it would likely end up with laminate over the top at some stage, and the paperwork lost.
Due to the other issues the op has, swa is really the only option in this case anyway.