Extending bonding for 2nd meter

JayAr91

~
Trainee
Hello,

A property has 2 gas meters (flats).

One is already bonded. Plan is to jump of this bond to get to the second meter. I know the cable has to be continuous.

What kind of join would you recommend?

I was thinking to use the current cable (currently from cu to meter 1) and go into a MET bar which id install inside the property but not next to the consumer unit. This met would be boxed in. From the met ill install 2 singles, 1 going to meter 1 and the other carrying on to meter 2? Good idea or can a alternative be recommended?
 
Last edited:
Strictly speaking BS7671 does not require it to be continuous. Your plan sounds fine but the earth terminal must be accessible. Personally I would extend the existing with a through crimp and split it at the first meter by just removing the insulation and not cutting it. Do these gas supplies serve the same dwelling?
 
Strictly speaking BS7671 does not require it to be continuous. Your plan sounds fine but the earth terminal must be accessible. Personally I would extend the existing with a through crimp and split it at the first meter by just removing the insulation and not cutting it. Do these gas supplies serve the same dwelling?
Thank you for your reply....property is a maisonette. I was thinking to do what you said, extending current cable but i feel like if i fit a met, its better for testing individually? Im guessing its not ok for it to be in the meter enclosure?
 