JayAr91
Trainee
Hello,
A property has 2 gas meters (flats).
One is already bonded. Plan is to jump of this bond to get to the second meter. I know the cable has to be continuous.
What kind of join would you recommend?
I was thinking to use the current cable (currently from cu to meter 1) and go into a MET bar which id install inside the property but not next to the consumer unit. This met would be boxed in. From the met ill install 2 singles, 1 going to meter 1 and the other carrying on to meter 2? Good idea or can a alternative be recommended?
Strictly speaking BS7671 does not require it to be continuous. Your plan sounds fine but the earth terminal must be accessible. Personally I would extend the existing with a through crimp and split it at the first meter by just removing the insulation and not cutting it. Do these gas supplies serve the same dwelling?
Upvote 0
Thank you for your reply....property is a maisonette. I was thinking to do what you said, extending current cable but i feel like if i fit a met, its better for testing individually? Im guessing its not ok for it to be in the meter enclosure?
Upvote 0
Do the maisonettes have separate supplies or do they come from the same source?
Upvote 0