Try a couple of new bulbs and see if they behave, would it be your responsibility to replace the fittings if your leasing?

Just the bulbs 1st to see if that works?

No, I suppose not. However he has said all the lights were working when we took the lease on. But i have told him about them before buit didnt progress with the issue.
 
General maintenance is likely to be your responsibility but yes replace a few tubes and see how it goes.
 
Depending on for how long you intend to occupy the building and how many hours the lights are on, you may well find the savings on energy costs go a long way toward the cost of the LED replacement, or indeed better. If that doesn't quite wash its face, you could capitalise the LED installation (whereas energy costs are a revenue charge to your P&L) and then you're only paying 25% of the LED replacement in year one but yielding the full benefit in operating costs...and do it at the start of your financial year.
 
Thanks again for the replies. The whole sequence thing is really strange. I am going to review CCTV to see if its the same sequence each night? I have uploaded a photo of one of the fittings leaning out the window.

20181030_173004.jpg
 
Honestly theres no need... As a few of us have said, this is what those type of lamp do at the end of their life, grab yourself a couple of replacements (size will be on bulb)
 
The arc tubes look to be blackening toward each end, a sign typical of end of life, as suggested by many posts on here.
 
Is that an e27 thread ?if so you can get led lamps that will fit though it does involve bypassing control gear,an easy job,lamps expensive but less than new fittings & labour.
 
Had this issue years ago on a old mod building and it was caused by individual photocells in the fitting reacting to light from other fittings switching them off and on as each light heated up and changed lux levels. If possible try disconnecting photocells and see if lights stay on just do a couple as test and go from there
 