So is a cpc required in an installation/circuit that relies on double or reinforced insulation for both basic and fault protection?


:)
 
Think about where you might have seen a circuit without a 'cpc'.

As a second year app I'm guessing you've probably seen a few.
 
Think about where you might have seen a circuit without a 'cpc'.

As a second year app I'm guessing you've probably seen a few.

Only some lighting circuits in older installations spring to mind. :smile:
 
That was allowed at one point. Not anymore.

Maybe im being mean as you could argue the immediate circuit I'm thinking off falls outside of 7671.
 
So is a cpc required in an installation/circuit that relies on double or reinforced insulation for both basic and fault protection?


:)

You could have Class 2 equipment that doesn't require an Earth, but .........
Or you could have a circuit which doesn't require a CPC, which would be ...?
Also, find the reg about taking a CPC to every point.
 
You could have Class 2 equipment that doesn't require an Earth, but .........411.3.1.1 still applies.
Or you could have a circuit which doesn't require a CPC, which would be ...? This is where im slightly confused.
Also, find the reg about taking a CPC to every point 411.3.1.1.

See bold text :smile:
 
If that dog hadn't ate that van with my regs book in I'd have nailed this one by now
 
So is a cpc required in an installation/circuit that relies on double or reinforced insulation for both basic and fault protection?


:)

Good question. :) Depends whether it's under effective supervision or not:

CPC_double_reinforced_insulation.jpg

Relevant regs: section 412, specifically 412.1.3 and 412.2.3.2.

I was wondering about the protective measure of electrical separation. Let's say for argument's sake, limited to the supply of one item of current-using equipment supplied from one unearthed source with simple separation (413.1.2). Reg 413.3.5 seems to imply that no CPC is needed. I'm not sure what value a CPC would have where electrical separation is used as the method of fault protection.

If you're looking for the reg that says you have to run a CPC everywhere*, then have a butchers at 411.3.1.1 <--- EDIT: I see this was answered in the time it took me to write all this. :)

* almost everywhere. Lampholders having no exposed-conductive-part hold a special place in our hearts...
 