ElectricalAsh

Hi I was asked today if it was possible to connect three 4" inch fans to one tile vent? I know that it could be done with a few bits of pipe and some draught stoppers to stop one fan blowing back down the other but would tile vent allow enough air to flow through with out causing problems with the fans? Has any one ever done this? Cheers ash
 
I have not done so,but here are my thoughts

I have seen older flat roof council house installations where bathroom/kitchen /toilet extracts to a central duct
They sometimes had a single fan in the duct to vent all rooms and sometimes had seperate fans in each room extracting into the same single duct,all had one roof vent serving all fans


I would think, smooth or wrinkled duct and length and size of duct would be the main restricting factor
Drip bends would also need to be considered

It would not look to pleasant having numerous tile vents popping up on the roof
 
Don't know what the application is, but have you considered a whole house recovery unit?
 
Cheers for the replies. Its for a small toilet block with two toilets and a shower room. The fans will be no further than two meters apart so the ducting run should be relatively short. not sure if it would work correctly with one in-line fan as the three fans are controlled by the three separate light switches. Think I will just have to give it ago and inform them that if it doesn't work correctly then two more tile vents need to be installed. Thanks again
 
what about if you get one of them pipe connectors they use in groundworks, goes all angles ..... as someone says dripss if going berticle/rising
 
I'm sure there was a similar thread to this one a few days ago.

If you have three autonomous fans into a single point, when only one fan is running it will be blowing into the other toilets as well as the intended discharge. I don't think one-way valves in the ducting will be effective.

Can't you fit a single fan with a single supply and install occupancy sensors in each toilet which are just wired in parallel. I'm sure this would be logistically simpler and probably cheaper.
 
What about one in-line centrifugal fan drawing from three pipes, triggered from any of the switch lines (might need to gang some contactors)?
 
What about one in-line centrifugal fan drawing from three pipes, triggered from any of the switch lines (might need to gang some contactors)?

If the lights are all on the same circuit it can be done without contactors

Using double pole light switches utilising one side of the switch as normal
The other side of the double pole fed from the load side of the first and out to the fan
Repeat for other rooms and single fan is then operated from any used light
 