joehat

I have a cu with a main switch/ faulty rcd, eg It doesn't trip under 5x 40ms and 1x 300ms.

As the board is an old one, without finding a replacement if ones possible, is it aloud that I put one in front of this rcd?

I don't see a problem myself, they don't want the whole new cu cost but would be happy with a new rcd before the board, leaving the rcd in the board that's not tripping with in max time.
 
I have a cu with a main switch/ faulty rcd, eg It doesn't trip under 5x 40ms and 1x 300ms.

As the board is an old one, without finding a replacement if ones possible, is it aloud that I put one in front of this rcd?

I don't see a problem myself, they don't want the whole new cu cost but would be happy with a new rcd before the board, leaving the rcd in the board that's not tripping with in max time.

How did you test the rcd?
 
If you are putting a new rcd in a seperate enclosure next to the cu i would bypass the old rcd but with all the messing about you might as well change the hole db with a split load plastic one as they are selling them off cheep and are still complaint until january , probley get one cheeper than an rcd in an enclosure
 

Reply to Faulty rcd in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
357
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
609
My friend just moved into a new build flat and its for a disabled person with a hydraulic lift to go to the upper floor. There was/is a leak...
Replies
8
Views
460
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
843
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock