132.16 No addition or alteration, temporary or permanent, shall be made to an existing installation, unless it has been ascertained that the rating and the condition of any existing equipment, including that of the distributor, will be adequate for the altered circumstances. Furthermore, the earthing and bonding arrangements, if necessary for the protective measure applied for the safety of the addition or alteration, shall be adequate.
If there is a fault on the light circuit that may cause extraneous conductive parts to become live then the earthing and bonding must be adequate; therefore if it is not adequate this must be addressed first.
Presumably if this is a class II light then the earthing and bonding would not need upgrading?