Hi does anyone know the type of the Federal “brown” 3871 breakers? The 3 poles have type 4 on them but nothing on the single poles? If they were type 4 the max zs of most circuits wont comply following our EICR.

Many thanks
 
You need to refer to manufacturers data for max Zs values.
 
does this help?
file:///C:/Users/tel/Downloads/Zesses-sheets.pdf
 
How easy will they be to find??
Impossible now as Federal Electric are no more. There are many internet Tables you can look at as per #6 but these can only be taken at face value. Merlin Gerin, Federal Electric, Square D and Dorman Smith were the most common producers and all quote variable maximum values of Zs so one Table does not cover all brands. Manufacturers Tables also quote 0.4sec and 5sec disconnection times. The attached fax came from Federal Electric many years ago, I have overwritten so it is legible.20180614_130400.jpg
 
Impossible now as Federal Electric are no more. There are many internet Tables you can look at as per #6 but these can only be taken at face value. Merlin Gerin, Federal Electric, Square D and Dorman Smith were the most common producers and all quote variable maximum values of Zs so one Table does not cover all brands. Manufacturers Tables also quote 0.4sec and 5sec disconnection times. The attached fax came from Federal Electric many years ago, I have overwritten so it is legible.View attachment 42774

Thats brill thank you very much for taking the time to assist!
 