Hello,
I am running a feed for a CU to an annex in the garden and just want to run things through with another sparky to make sure all is correct.
The main consumer unit in the house is fed from a 100 amp main fuse and all circuits are RCD protected on a split load plastic board.
The annex will have a 9kw electric shower, a 3kw steam generator for a steam room, 5 double sockets (there will probably be a couple of oil radiators plugged into these) and 4 lights.
Assuming the oil filled radiators are 3kw, the max demand is around 80 amps.
Feasibly, this could be pulled all at once too, with someone in the shower, two radiators on full blast, and the steam generator on.
Would you install an 80 amp fused isolator for this installation?
Could this setup potentially cause the main fuse to blow if the annex was at full load and someone used an electric shower in the main house?
It seems like a heavy load, especially as its a large family and it is feasible that the above scenario could happen.
Let me know your thoughts.
Many thanks.
Hello,
Many thanks.
I think you have answered your own question. To cover yourself, get supply changed to 3-phase. Then do volt drop calculation for length of run and determine what size armoured you need, 16mm or 25mm. Unless you want to change your phone number after the job and preferably move to another part of the couintry.
Upvote 0
Hello,
Many thanks.
Have you applied diversity to the maximium load
Upvote 0
Hello,
Many thanks.
Has this annex been wired yet ?
How far away from the house is it ?
What earthing system ?
Upvote 0
The annex is already wired by another electrician.
There is a 10kw shower, 5 socket outlets on a ring, and a lighting circuit feeding 4 lights.
It's around 10 metres from the main fuse to the new consumer unit in the annex.
The earthing system is TNS
Upvote 0
This is what I was considering, but should diversity be applied when you have a strong opinion that several high loads could be used together?
For example, there is an electric shower in the annex. I saw several electric heaters in there too.
There is an electric shower in the house and several electric heaters. It seems they prefer to use electric heaters in one or two rooms rather than the central heating.
There is also an EV charger.
This is a family of 6.
2 electric showers running together pull around 80 amps alone.
Add a few heaters on, and you are past the 100 amps of the main fuse.
I know the fuse won't blow at 100 amps, but isn't it beat practice to use that number as the maximum load after applying diversity?
Upvote 0
Thank you!
Upvote 0
Hello,
Many thanks.
You could consider load limiting devices.
Upvote 0