Hello gents I need your help plz.

Lets suppose we have 15 led lights bulbs on a 2 core cable. I chopped 5 of them coz it was too long for the job. Now 7 out of 10 work and the last 3 don't work. When I touch the two ends together the last 3 switches on and the first 7 turns off.
How can I make them all work.
 
Seems they are in series-parallel groups with the first seven in series, the last eight in series, and those two groups in parallel across the driver. When you cut off the last three, you broke the circuit of the second group and only the first group lit. When you completed the circuit by shorting the two ends, the group now consisting of only three lamps had a much lower forward voltage than the group of seven, so the current supposed to be flowing in the first group was diverted to the second as well (with the lamps probably running at double their rated current.)

The series-parallel connection makes things much harder to modify. If the driver's voltage compliance range includes the forward voltage of five lamps, you could rewire as two parallel groups of five. Alternatively you could ballast the second string to compensate for the missing lamps, but with heat dissipation and energy wastage equal to the power of the missing five lamps. Or maybe just extend the leads to reconnect the original 5 lamps in a position that their light can be utilised.
 
Last edited:
Seems they are in series-parallel groups with the first seven in series, the last eight in series, and those two groups in parallel across the driver. When you cut off the last three, you broke the circuit of the second group and only the first group lit. When you completed the circuit by shorting the two ends, the group now consisting of only three lamps had a much lower forward voltage than the group of seven, so the current supposed to be flowing in the first group was diverted to the second as well (with the lamps probably running at double their rated current.)

The series-parallel connection makes things much harder to modify. If the driver's voltage compliance range includes the forward voltage of five lamps, you could rewire as two parallel groups of five. Alternatively you could ballast the second string to compensate for the missing lamps, but with heat dissipation and energy wastage equal to the power of the missing five lamps. Or maybe just extend the leads to reconnect the original 5 lamps in a position that their light can be utilised.
Thank you,
That is exactly what it is. We tried to connect a 800ohms resistor at the end which actually worked.
 
As long as you know what you're doing...

giphy.gif
 

Reply to Festoon lights outdoor in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I replaced an outdoor electrical socket recently with a 2 gang, BG socket which has LED lights to show when it is switched on. Since then I...
Replies
19
Views
392
I am installing 9 LED downlights each with an RGB bulb in (i will try attach pictures on them) - anyway I have been told that they need to be...
Replies
4
Views
729
I have a street light circuit on land I rent out. I need to replace 2 of the bulbs. 1 of them is an old Philips 55W SOX Plus, the other is a...
Replies
3
Views
504
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
776
Hi I've been planning to fit an outdoor junction box at the front of my house to hide a large brickwork hole and properly house the wiring...
Replies
9
Views
833

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock