i=p/u

I have 35mm 5c swa protected by 63A fuses at source, there is isolator along the circuit with 160A fuses, should these have been removed and links put in instead?


Also I have a ze 0f 0.07 and a zs of 0.11

There is about 50m of 35mm line and cpc @ 1.048 x 50/1000=
 
The 160A fuses are at no risk of blowing (total selectivity with 63A) so no benefit from changing to links, except perhaps to let folks know "these are not the fuses you are looking for..."

You could always label it to that effect.

Is this a final circuit or a sub-main?

For sub-main pretty sure it meets 5s disconnection without checking based on your Ze/Zs but not looks at for final and 0.4s. If it is a sub-main you might want to consider a bigger source fuse to get better selectivity with larger MCBs, but of course not if it is serving to protect a supply DNO fuse from risk.
 