the pict

~
Mentor
OK was asked to do the wiring from panel to heads, sounders and remote indicators no prob as the design was already done and commisioning to be done by the company that does the routine tests,
So now that this new building has had it first occupants and because the heads are mounted right outside the toilet/shower room they trigger with steam,
(something I mentioned at the outset), anyway I have been asked to move the heads farther into the room above the beds, now the design guy says that the FP cannot be joined to extend the reach is this the case ? I dont mind as it is more work for me, but I assummed that there would be FP enclosures for this purpose ?

Pict
 
Standard 20mm gav through boxes with stuffing glands are fine, as long as the cables are crimped.....Bad design on the fire company`s behalf tho, they should be aware of proximity to bathrooms.
 
This is a modular building assembled in a factory and erected on site with all cable trays conduit etc in situ but yeah should have been picked somewhere along the line,maybe I should have said more,
Pict
 